Glenn Stanton

we no longer have the setup criteria for that burner/boiler combination. We do have the Wayne and Carlin setup data and they both call for a 2.50-60 or 2.75-60 Solid nozzle for low and high firing rates. Hope this helps.

Glenn

Comments

  • Greg_11
    Greg_11 Member Posts: 16
    Glenn Stanton

  • Greg_11
    Greg_11 Member Posts: 16
    Glenn Stanton

    I'm having a problem with a burnham V-36 steam boiler with an ABC/Sunray Bantam FC-234 burner on it.Was wondering if you have any specs on this laying around?
  • Greg_11
    Greg_11 Member Posts: 16
    Glenn Stanton

    I'm having a problem with a burnham V-36 steam boiler with an ABC/Sunray Bantam FC-234 burner on it.Was wondering if you have any specs on this laying around?I found some info on "Just for Techs" (http://www.jcgbs.com/users/jft/abc-sr.htm#Bantam "FC" Series).
    Two things i need are correct nozzle, and pump pressure.I'm assuming 100 psi.The nozzle in it now is a 2.00-60B.The boiler lable calles for 2.6 or 2.8 GPH input, but the burner lable says 1.00 to 2.00.Evidently someone has downfired it.Everything on the steam side is working fine,but the end cone keeps getting coked up and shorts out the electrodes.And the fire is off center to the left and impinging on the side of the boiler a little.
    Any specs or advice you can give me would be appreciated!Homeowner does'nt have the book(like that's something new!).Thanks.
  • Steamhead
    Steamhead Member Posts: 17,387
    Burnham OEM Bantam specs

    These are from the V1 series installation manual but they might help. They already helped out one Wallie, let's go for two. Note that the 2.00 and 2.25 GPH nozzles are specified as solid-cone 45-degree rather than 60-degree, this may explain the impingement problem you're having.

    I have an FC-134 on my V-14 and it works great.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Greg

    I will get you those specs tomorrow and post them here. I wouldn't go by the specs that were posted for the V-1 as the V-3 is quite a different boiler and had 2 firing rates per size. Hope this helps.

    Glenn
  • Greg_11
    Greg_11 Member Posts: 16
    steamhead

    Thanks for the info.That 45 degree might be the ticket.
    Definately worth a try.
  • Steamhead
    Steamhead Member Posts: 17,387
    Since Glenn is here

    why not wait for him to dig it out of the Burnham files? He's usually pretty quick to do so, and you'll know for sure when he does.

    The same thing happened to my burner when a tech stuck an 80-degree nozzle in it by mistake- the retention head got all coked up. He was used to Becketts!

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Greg_11
    Greg_11 Member Posts: 16
    great

    Thanks glenn. That will be a big help.The smaller firing rate stamped on the boiler is 2.60 GPH.Do you think that it is downfired too much at 2.00? I've heard before that you should try not to downfire more than 20%.If this is true, this one is right on the edge.It's been heating fine at 2.00GPH so i have'nt got the urge to measure EDR,figuring that someone oversized the boiler when it was replaced,and i would just end up with a smaller firing rate anyhow.Thanks again for your help!
  • I believe

    that the V36 had equivalent firing rates of 2.60 gph and 2.80 gph. I'll take a look at the original specs and if we have any downfire specs that have been tested and approved, I will post them also. Talk to you tomorrow.

    Glenn
  • Steamhead
    Steamhead Member Posts: 17,387
    Glenn, if I find one of those in my travels

    I'll scan and e-mail it to you.



    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Found it!

    I had one of our guys here in New England hit the archives of one of our distributors and I got it today. Here you go! The nozzles used on the FC-234 in the V36 were 2.50-30-P and 2.75-45-P. They are distinctively different than the Carlin and Wayne specs. Hope this helps.

    Glenn
  • Greg_11
    Greg_11 Member Posts: 16
    Thanks

    For taking the time to look.I'll get it tuned in one way or another.If everything was easy ,i'd probably get bored anyhow!:)
  • Greg_11
    Greg_11 Member Posts: 16
    Your the man!

    Thank you very much!