steam in the return
ceikey
Member Posts: 60
of my steam system. The LR radiator is getting hot on the return side first. For some reason I am getting steam through the return??? How worried should I be about this? How can I fix it? I appreciate any help!
0
Comments
-
Didn't come thru
try converting to a .jpg file if you haven't already, and try again.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
try this
0 -
Combination One-pipe/Two-pipe, air-vent system
is what you have there. Steam is getting thru the radiators close to the boiler, then going thru the return and entering the living room radiator the wrong way, aided by the air vent on the return.
There should not be an air vent on the return in this system. Relocate that vent to a point on the steam main near where the living room, dining room and two second-floor radiator takeoffs come together. This will get the steam to that point quickly, and assuming the vent is properly sized, the system will be much better balanced.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
thanks
That makes sense. I am renovating the bathroom and have the radiator out and the problem seems to have gotten worse. The steam probably gets to the return even faster with it out because less radiators are being fed.0 -
If the return valve leaks
cap off the pipe. With the radiator out it is probably acting like an air vent.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 914 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements