Pigtails
Dave_23
Member Posts: 190
I'll be working on my boiler's pigtail soon. Should I leave it dry, or prime it with a little water to separate the gauges/vaporstat from the steam.
If so, how much water is recommended?
Thanks, Dave
If so, how much water is recommended?
Thanks, Dave
0
Comments
-
Very Few...
... get installed with the pigtail already primed with water, even on high pressure industrial systems. I've seen a couple of really expensive industrial instruments that require the loop to be filled with water prior to starting the system up, but even on 250 and 300 PSI systems, they usually just get installed dry. The steam quickly condenses in the loop as the pressure comes up, and it fills with condensate before much pressure is on the system.
The sole purpose of the pigtail is to keep steam temp off the internals of pressure gauges, etc. I've seen gauges installed on steam systems without pigtails, and they'll still often work for a few weeks. You can't overfill them, so if you feel more comfortable filling the pigtail with water, it won't hurt anything. Any little bit of excess water will just drain back into the boiler or steam line.0
This discussion has been closed.
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 926 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements