Vaporstat Setting & Boiler Operation
Dave_23
Member Posts: 190
Folks,
In my vapor system, I will be substituting a L408A1132
vaporstat for the stock pressuretrol.
It was recommended that I start with the following vaporstat settings: Cut in at 4 oz, Differential at 6 oz.
Given that this is a subtractive type device, is the following operating profile correct:
Upon call for heat, the boiler steams to a maximum of 10 oz pressure, at which time, the boiler shuts off. When the steam pressure drops to 4 oz, the burner refires. All this is assuming that the thermostat is continuously calling for heat.
Correct?
-Dave
In my vapor system, I will be substituting a L408A1132
vaporstat for the stock pressuretrol.
It was recommended that I start with the following vaporstat settings: Cut in at 4 oz, Differential at 6 oz.
Given that this is a subtractive type device, is the following operating profile correct:
Upon call for heat, the boiler steams to a maximum of 10 oz pressure, at which time, the boiler shuts off. When the steam pressure drops to 4 oz, the burner refires. All this is assuming that the thermostat is continuously calling for heat.
Correct?
-Dave
0
Comments
-
yes
see if all of the radiators still get hot and if so, that's all there is to it.0
This discussion has been closed.
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 926 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements