Steam Vents

Options
Steamhead
Steamhead Member Posts: 16,889
you can bet I'll call tomorrow to request a copy!

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=157&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting

Comments

  • Bill Riordan
    Bill Riordan Member Posts: 1
    Options
    Steam Vents

    I Just left a job with one pipe steam system. First floor heats well and satifies thermostat on first floor before radiation on second floor can heat up enough. All radiators have new Hoffman # 40 vents and new main vents.Any ideas on how to balance system?
  • tp tunstall
    tp tunstall Member Posts: 63
    Options
    steam vents

    give my office,(manufacturing plant) a call, ask for chris shea, and request a booklet called Venting is everything" he'll mail it to you, no charge. published by Dole. tel # 1-800- 423-55878. tell him i suggested this. regards, tp tunstall
  • Boilerpro
    Boilerpro Member Posts: 410
    Options
    A souple of things to look at...

    ARE the main vents sized to the piping and is the boiler small enough to work in harmony with the system? Also, 2nd floor vents need to vent the air in those tall risers, so they need to be bigger. Some of the many adjustable vents out there will work well. For vent sizing get the Deadman's steam heating video and workbook at Books and More.

    Boilerpro