short-cycling steam boiler
Glenn Harrison
Member Posts: 405
Assuming that the guage is accurate, if the guage never reads 1 psi, and the pressuretrol is set at 3 psi, It shouldn't be the pressuretrol. Have you by chance replaced or done work on the thermostat recently, or had other work done to the boiler controls? This sounds like the thermostat anticipator is set way too low. What kind of thermostat do you have? Another possibility, do you have electronic ignition? There may be a problem with this also.
Glenn Harrison Residential Service Tech
Althoff Industries Inc. Mechanical and Electrical Contractors
Crystal Lake, Illinois
Glenn Harrison Residential Service Tech
Althoff Industries Inc. Mechanical and Electrical Contractors
Crystal Lake, Illinois
0
Comments
-
short-cycling steam boiler
My home boiler (70000 BTU) cycles on and off very quickly -- it'll run for as little as 1 minute then shut off -- then a few minutes later come on again.
Possibly related: the pressure gauge has never read higher than 1 PSI. I removed the pigtail connecting the Pressuretrol to the boiler the other day. It was plugged-up with sediment and I cleaned it out and re-installed it. Still, the pressure gauge never reads higher than 1 PSI. I have the Pressuretrol set at around 3 PSI.
The boiler generates plenty of steam when it runs...though it's not reaching the radiators furthest down the line even though I just installed a main vent at the end of that line.
I think if the boiler ran for a longer continuous cycle steam would get to the furthest radiators.
Any ideas?
thanks -- Larry
0 -
short cycling
set the pressuretrol for .5 on the scale and 1 on the differantial wheel inside the control the less steam pressure the better other than that find someone who understands steam
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
try these two things
since you have a new main vent try first- you cleaned the pigtail, but how about the inlet to the pressuretrol? clean it and blow in it. you should be able to hear it click the switch when you blow into it. and second- skim the boiler to clean up the water. check its ph also.0 -
Is the main vent hot before the boiler short cycles?
If it isn't, you aren't venting as fast as you are steaming, and you are shutting off on the back pressure of the air against the vents. More venting would be called for. You can probably hear the system venting, which is a symptom of too little venting capacity, if this is the case.
Noel0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements