boiler ph
terry_6
Member Posts: 17
Any recomendations on boiler additives to lower the ph of a 1 pipe steam system. It's currently 13+
0
Comments
-
could use
swimming pool chemicals. available just about anywhere. mix it with water then pour into boiler. you dont usually have to even know a scientific name as its usually marked PH DOWN on the bottle. its what i use. there is also a ph up.. you may want to pick up a jar of both in case you overshot the mark. hope this helps0 -
High Ph
Before you do anything you had better find out what caused this to happen.
Ph above 11 usually is accompnied by sudsing in the boiler.
This would make the water level very unstable and the you could have or should have short cycling.
To be safe re-check the Ph of the water with an electronic Ph sensor. Some times one extra drop of re-agent gets into the test device and the test is not accurate.
Jake0 -
Thanks, the only thing I can think of is that after cleaning the boiler I didn't flush the chemicals out well enough; leftover caustic soda would do it. I'm continuing the flush now; feed water ph is 7.5...0 -
jacob, could you expain how the short cycling
takes place with high ph, i think i ran into that last week. perhaps. i had a boiler short cycle and wasn't sure why. i first looked for air problems, then i drained, refilled and skimmed the boiler. problem was gone then but i wasn't sure what had happened or for that matter exactly how i fixed it. it was one of those blind luck things.0 -
TSP (ph 11) and other
soap based cleaners could cause the high ph you are seeing. I'd flush a few more times and see what happens. I think it would be better to flush out the cleaners than buffer the ph with the soap still in there.
Check with the boiler manufacture, on hydronic system they recommend a ph of 7.5-8.5. Not sure about steam, however.
hot rod
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
pH steam
8-9 is good, virtually the same. If you can, check the condensate coming back for pH. The boiler water is a collection of everything in the system, and the returning condensate is sometimes different in pH. The boiler water can be flushed and changed, or treated if it isn't where it should be.
Noel0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements