taco problem
MIKE6
Member Posts: 102
3 zone system,one zone baangs wwhen the unit stops calling for heat.One circulator,3 taco zone valves.Any ideas?
0
Comments
-
Check...
the directional flow arrows on the zone valves. They WILL hammer if they're being flow through backwards.
ME
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0