commercial steam boiler
ed wallace
ed wallace Member Posts: 1,612
working on a commercial steam bioler in a church 2 pipe system am wondering can i replace the p404a pressuretrol with vaporstat and run it on lower pressure than 2 1/2 pounds any help would be appreciated
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=256&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
  • You sure can, Ed.
    If you think you may need more than one PSI, there is one that goes to four PSI. The 0-16 ozs. one is a lot more sensetive below one PSI, though.
    Here's some numbers....
    L408A1132 Honeywell....SPST and breaks on rise.... 0-16 ozs.
    L408A1157 Honeywell....SPST and breaks on rise.... 0-4 PSI
    Steamhead Member Posts: 18,209
    But make sure
    your main vents (or crossover traps, if used) are properly sized and working OK. Otherwise you may encounter steam distribution problems at the lowered pressure. You should be able to vent the mains in about a minute on about 2-ounces pressure.
    When you get everything set up properly, the system will run on considerably less fuel.
    Consulting