hw zone off steam boiler noisy

I installed a hw zone on my steam boiler to feed new space on my third floor. I have two circs pushing the water, and used 3/4 inch copper. It clangs loudly during colder days and nights. I have no bypass line in it...would installing such a line eliminate some or all of the noise? Any other suggestions?

Thanks in advance.

Comments

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,598
    It needs a bypass

    and there's probably no reason for two pumps in series. You're not lifting the water to the top; it's circulating.

    Click on Heating Q&A and read the section called, "Condensate Hot Water Heating."
    Retired and loving it.
  • jcmoretti
    jcmoretti Member Posts: 3


    thanks.
    On the bypass, can I use standard tees or do i need a monoflow on the return side?

    jcm
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,598
    standard

    tees are just fine.