Bob Tonner
Bob Tonner Member Posts: 64
Partial List of Features:
1. Same size and mounting as Honeywell 8124
2. Flip open lid, with easy access for wiring
3. Lighted text display that shows:
a)Boiler Temperature
b)Burner Status
c)T-T status
d)X-X/ZR status
e)C1-C2 status
f)ZC status
g)DHW or Injection loop temperature
h)Remaining Warranty Period(counted down in weeks, only when control is energized.
4. Restricted access setup menu that allows installer to:
a) Digitally adjust High Limit (120-220 F)
b) Digitally adjust Low Limit (off, 100-180 F)
c) Digitally adjust Differential (10-60 F)
d) Select "Auto" Mode which adjusts high limit, low limit and differential based on heat loss profile on a continuous basis.
e) Select Pump configuration:
i) L-8124 (default configuration, just like you're used to)
ii) Injection (configures ZC as variable speed injection controller that maintains loop at temperature set by installer, with and sensor input
iii) i-DHW (configures ZC as dedicated indirect loop that maintains indirect DHW tank at temperature selected by installer, with sensor input.
iv) Priority (makes ZC priority pump and X-X priority input)
5. Completely Solid-state (no relays to fail)
6. Same price as an 8124

This is only a partial list of features.

Bob Tonner
President
InfinityLab Inc.
(905) 619-0837

Comments

  • Bob Tonner
    Bob Tonner Member Posts: 64
    Spy Photos

    New Boiler Control in final stages of development.

    Operational details are yet to be announced, but we assure you that you will be impressed.

    Bob Tonner,
    President,
    InfinityLab Inc.
  • hr
    hr Member Posts: 6,106
    Will the

    O-Scope be included? :) Don't leave us hanging to long.

    hot rod

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Bob Tonner
    Bob Tonner Member Posts: 64
    Hydronix Boiler Control

    Partial List of Features:

    1. Same size and mounting as Honeywell 8124

    2. Flip open lid, with easy access for wiring

    3. Lighted text display that shows:

    a)Boiler Temperature

    b)Burner Status

    c)T-T status

    d)X-X/ZR status

    e)C1-C2 status

    f)ZC status

    g)DHW or Injection loop temperature

    h)Remaining Warranty Period(counted down in weeks, only when control is energized.

    4. Restricted access setup menu that allows installer to:

    a) Digitally adjust High Limit (120-220 F)

    b) Digitally adjust Low Limit (off, 100-180 F)

    c) Digitally adjust Differential (10-60 F)

    d) Select "Auto" Mode which adjusts high limit, low limit and differential based on heat loss profile on a continuous basis.

    e) Select Pump configuration:

    i) L-8124 (default configuration, just like you're used to)

    ii) Injection (configures ZC as variable speed injection controller that maintains loop at temperature set by installer, with and sensor input)

    iii) i-DHW (configures ZC as dedicated indirect loop that maintains indirect DHW tank at temperature selected by installer, with sensor input.)

    iv) Priority (makes ZC priority pump and X-X priority input)

    5. Completely Solid-state (no relays to fail)

    6. Same price as an 8124

    This is only a partial list of features.

    Bob Tonner, President, InfinityLab Inc., (905) 619-0837
  • hr
    hr Member Posts: 6,106
    Send one my way

    I'll give it the old contractors once over. I like being able to adjust the boiler on/ off diff. This would be handy for a large shop project I am going to run a 40 degree Delta t on the two staged boilers.

    Did you say a post purge pump relay is in the brain also? Adjustable?

    hot rod

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Bob Tonner
    Bob Tonner Member Posts: 64
    Post purge Pump Relay

    It is selectable in the menu-driven setup. I'll put you on the early prototype list for this winter.

    Bob Tonner
    President
    InfinityLab Inc.
  • Bob Tonner
    Bob Tonner Member Posts: 64
    Where are you located?

    Are you in the Northeast USA? We are making a road trip soon and would be glad to show a live working model (of the control that is).

    Bob Tonner
    President
    InfinityLab Inc.
  • jim f
    jim f Member Posts: 182


    how about an approxamite price on such an item??
  • Bob Tonner
    Bob Tonner Member Posts: 64
    Pricing

    We cannot be specific at this time, but suffice it to say that you will NOT pay more than you are currently paying for a Honeywell 8124 or 7124. It will likely cost more than a 8148.

    Best regards
    Bob Tonner
    President
    InfinityLab Inc.
  • Would love one for my training center

    to use for training techs. If this is going to be used in the future on boilers I love to get in on the ground floor on new technology. I have actually been talking about the need for a control that does what your control is offering. Get in touch with me at:

    Timmie M. McElwain

    Gas Appliance Service Training and Consulting

    22 Griffith Drive

    Riverside, RI 02915

    401-437-0557

    FAX 401-270-1893
  • Bob Tonner
    Bob Tonner Member Posts: 64
    You are on the sample list

    Timmie,

    The first version available will be Oil Heat only. The Gas version will be hot on the tail of that one. But, for training purposes they have the same operational characteristics.

    Bob Tonner
    President
    InfinityLab Inc.
This discussion has been closed.