Shocking Of Boiler Sections
steve curran
Member Posts: 6
Where I Work All Our Boilers Are Gas Fired Hot Water With Oil Back Up. The Last Few Years A Cast Iron Section Will Crack. Any Answers Out There What Will Cause This. Is This Cause By Shocking Of Low Water Return Temperature. Looking For Solutions For this Problem. Steve Curran
0
Comments
-
cracked sections
sounds like low return temps you need to install a bypass between the supply and return the owner of local supply house recommends a 3/4 line between supply and return with ball valve to throtle amount of water thru bypass0 -
read HB Smith problems, postings0 -
Are they staged fired...
with each boiler having it own circulator and piped Primary/ Secondary? This popular installation configuration leads to both cold shock from cold system return temps, and hot shock whan a cold boiler is staged on and the system is already hot. Been replacing alot of cracked boilers due to this piping layout.
Boilerpro0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements