Viessmann Help
Mark Wilson
Member Posts: 8
We are putting in a Vitola. Can you run regular solid thermostat wire to the Reset stat or do you need stranded. All of the other expansion bus components use stranded wire.
Thanks,
Mark
Thanks,
Mark
0
Comments
-
wire
do you mean to the outdoor sensor??? If so yes solid wire is not an issue we've used it for years no problems0 -
Thermostat wire
Are you talking about the outdoor sensor? All we ever use is 18 gauge solid wire and it works fine.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
RFI issues
Viessmann recommends the use of 18/3 shielded thermostat wire for both the outdoor sensor or RC thermostats. With many homes being "wired" with both cabling or alarm systems, stray RF signals have been found to interfere with the computer. The shielded wire costs a few cents more per foot, but will prevent any future glitches.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements