Injection Loop Size
Patrick_3
Member Posts: 20
Goodmorning Gentlemen,
I have been reading up on the injection system and I think I have it on paper and ready to begin building up, but would like a second opinion. System will have a total of 5 radiant zones and 2 high temp zones.
Radiant zones are designed with 20 delta T and 105* supply.
Zone 1 (garage) 1.5gpm, 3.4 head, 15100 btu
Zone 2 (main fl) 1.6gpm, .9 head, 16269 btu
Zone 3 (master) .7gpm, 1.2 head, 6631 btu
Zone 4 (bed rm) .6gpm, .7 head, 6139 btu
Zone 5 (basemt) .8gpm, 1.4 head, 8330 btu
Zone 6 Indirect water heater
Zone 7 20ft baseboard
Using design procedure from tekmar manual:
Boiler supply temp (Tb)= 180*
System supply temp (Ts)= 105*
Tb-Ts = 75*
System flow rate = 60,000btu @ 20delta T = 6gpm
Flow ratio = .20
Injection flow rate (6gpm x .20)= 1.2gpm
According to the desing table my injection loop could be made up of 1/2" copper, taco 007 circulator and a globe valve to throttle flow.
Looking for a little assurance before I begin, thanks, Patrick.
Was hoping to meet up with some of you at the ISH convention, but due to employees not wanting to work (I guess sitting at home pays better than $15.00/hr) I had to cancel my trip.
I have been reading up on the injection system and I think I have it on paper and ready to begin building up, but would like a second opinion. System will have a total of 5 radiant zones and 2 high temp zones.
Radiant zones are designed with 20 delta T and 105* supply.
Zone 1 (garage) 1.5gpm, 3.4 head, 15100 btu
Zone 2 (main fl) 1.6gpm, .9 head, 16269 btu
Zone 3 (master) .7gpm, 1.2 head, 6631 btu
Zone 4 (bed rm) .6gpm, .7 head, 6139 btu
Zone 5 (basemt) .8gpm, 1.4 head, 8330 btu
Zone 6 Indirect water heater
Zone 7 20ft baseboard
Using design procedure from tekmar manual:
Boiler supply temp (Tb)= 180*
System supply temp (Ts)= 105*
Tb-Ts = 75*
System flow rate = 60,000btu @ 20delta T = 6gpm
Flow ratio = .20
Injection flow rate (6gpm x .20)= 1.2gpm
According to the desing table my injection loop could be made up of 1/2" copper, taco 007 circulator and a globe valve to throttle flow.
Looking for a little assurance before I begin, thanks, Patrick.
Was hoping to meet up with some of you at the ISH convention, but due to employees not wanting to work (I guess sitting at home pays better than $15.00/hr) I had to cancel my trip.
0
Comments
-
Yep!!
Seems right to me..
And I sympothize about your employees..
KCA :-):-) Ken0 -
i did the calculation at 1.5 gpm
the max for half inch pipe, it would provide a blended temperature of about 112 degrees useing the full gpm. so you will be less, as you already figured out,,your correct as far as i can figure with pencil/paper.0 -
About right
What's a few 1/10's between friends! At that flow rate, and zip for pressure drop, shop for a smaller pump or you will end up throttling away most of that 007. Seems silly to throttle a 10 gpm pump down to 1.2 gpm! A 003 would be plenty, less electrical consumption and less throttle needed.
I'm going to these small balance valves with the little flow indicators for the balance valve. You get a nice fine adjustment, (needle valve) and some pressure drop to help that pump
You could probably inject enough through a 3/8" lines and run the pump up curve even further.
I'm also installing the pump on the return side these days so it runs in 105 degree temperatures instead of 180. Not a big deal, but why not. The throttle valve goes on the high temperature supply riser.
I'd throttle those employees a bit while your at it :0
hot rod
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Who makes that valve?
HR who makes that valve?0 -
Thanks
for being there when a guy needs a second. I will check on the 003 pump and the balance valve. Once again I thank you and best too all!! Patrick0 -
The valve
is available from Watts Radiant, Flowguard. I believe it is a Dumser which is now a Watts company. Oventrop may have a similar valve also. There are a bunch of these out there this is the first I have seen with the little window.
hot rod
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
ISTEC
at www.istec-corp.com also shows that same valve.
hot rod
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Fell Off My Seat
I'm a contractor and I have been absorbing the wealth of knowledge that you 'regulars' bring to this site. Thanks,sincerely. I've had a few chuckles but hotrod's comment about throttling at the end of a very concise and thorough response made me laugh so hard I fell off my chair.0 -
stinking employees!!!!
Can your employee's actually afford a home making 15.00 an hour???? I'd take the money saved from not going on your trip and spread it out amongst the men! I guess they know they can never be fired....seeing how slaves have to be sold0 -
Helper
> Can your employee's actually afford a home making
> 15.00 an hour???? I'd take the money saved from
> not going on your trip and spread it out amongst
> the men! I guess they know they can never be
> fired....seeing how slaves have to be sold
0 -
Frank
What do you pay for helpers. These are first and second year aprentice, no hvac schooling except what I pay to send them to and spend to train them. It hasn't been 15yrs since I left the farm milking twice a day and throwing hay for 8hrs in between for $3.00/hr no overtime pay either. Oh yea, vacation? holicay pay? right!! Journey pay is $25.00/hr. With out knowing what I've done for these guys I believe your attitude is out of line!! Patrick0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements