Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Saw something Weird
Larry_7
Member Posts: 86
Went to relight pilots after gas off by Street Dept. Big house. Pretty big steam boiler. Didn't note input. Anyway, it had a Taco zone valve installed below the flush valve on the LWCO. From there, it was piped to a drain. ZV was wired to a one of those cheap adjustable solid state delay relays and from there to a control panel on the wall. Anybody seen a set-up like that? I assume it's a way to automatically flush the control. Must be on some type of timer. The flush-valve handwheel appears still intact. Appears to me even if the ZV opens, somebody's hand would still need to turn the valve. I just haven't seen such an arrangement before and got me to wondering. I do that a lot.
Larry
Larry
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements