Pump Size Help
Jay C.
Member Posts: 5
Hello Wall! It's been awhile, hope you're all doing well.
I just walked into the middle of a job in which a plate heat exchanger being used to cool system water for a number of Climate Master heat pumps is being taken off well water and put onto a cooling tower.
The tower has been set and the pipeing run down into the boiler room. The first question I asked was "Where's the pump?" to which I got blank stares in return. I called the company who made the exchanger and spoke to the engineer, who gave me the relavent data to use in sizeing up the pump. Only problem is I'm not sure what to do with the data and the Local B&G rep's engineer is nowhere to be found today. So here I am, in the hopes that y'all will take pity on me and lend a hand.
Heat Exchanger: Req'd GPM = 75
Pressure drop = 2.3 psig
Pipeing: 270 feet (counting elbows) of 3" SCH 40 PVC in each direction with a rise of 20 feet.
Pump suction to be connected to heat exchanger discharge to pump water up to tower set in parking lot, per the manufacturers instructions.
Thanks for any help you can give.
JC
I just walked into the middle of a job in which a plate heat exchanger being used to cool system water for a number of Climate Master heat pumps is being taken off well water and put onto a cooling tower.
The tower has been set and the pipeing run down into the boiler room. The first question I asked was "Where's the pump?" to which I got blank stares in return. I called the company who made the exchanger and spoke to the engineer, who gave me the relavent data to use in sizeing up the pump. Only problem is I'm not sure what to do with the data and the Local B&G rep's engineer is nowhere to be found today. So here I am, in the hopes that y'all will take pity on me and lend a hand.
Heat Exchanger: Req'd GPM = 75
Pressure drop = 2.3 psig
Pipeing: 270 feet (counting elbows) of 3" SCH 40 PVC in each direction with a rise of 20 feet.
Pump suction to be connected to heat exchanger discharge to pump water up to tower set in parking lot, per the manufacturers instructions.
Thanks for any help you can give.
JC
0
Comments
-
Hi Jay, If you go to the follwing link you can plug in your numbers and come up with your answer. The site is very well put together.
http://appserver.ittind.com/software/plus/ESPinscreen.htm
Your friend in the industry,
Alan R. Mercurio0 -
Thanks
Alan !0 -
75 gpm @ 35'
looks good to me --Series 60 2x61/4 1hp B&G0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements