Trying a mini tube system hr

Options
hr
hr Member Posts: 6,106
This remote manifold station will provide heat for a 10,000 sq. ft. shop. I will inject 9.5 gpm either with copper or 1" Kitec from the mechanical room about 60 feet from the manifold location.

Had I thought of this sooner I would have had Lee at Speed Header custom fab the entire manifold without having to use any threaded fittings, except the flanges and filterball. I may stick a Spiro vent on this arrangment also.

A circuit setter flowmeter on the injection supply will allow me to dial in the correct injection GPM.

Two cast iron 200,000 boilers will supply the power. I'll try to run a 40 degree delta T, stage, rotate, and post purge with some of the new tekmar controls.

This method will save me about 130' of 2" copper and insulation, to be replaced with the 1". A good method to keep in your "bag o tricks" for moving lots of BTUs long distances.

hot rod

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>

Comments

  • keith
    keith Member Posts: 224
    Options
    mini-tube

    any body try a variation of this for a condominium application? Have 5 buildings with 5 units in each.
  • joe_14
    joe_14 Member Posts: 138
    Options
    sounds great



    Hi Hot Rod.

    Iread the wall a lot .Have read many of your post in the past,have got some good ideas from you. This job sound like it should work like a charm. Post pictures of completed job


    good luck