Primary Secondary sizing
Options
Alan(CaliforniaRadiant)Forbes
Member Posts: 1,243
is usually very small, we typically use a Taco 005 on small, medium and even large systems. It will handle 15 gpm at 4' of head which is 150,000 BTU's at a 20* delta T; that's a lot of heat.
As far as lifting the flow checks, if you pipe with closely spaced tees off your primary loop, the pressure differential created by the primary pump will not "see" any secondary piping.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
As far as lifting the flow checks, if you pipe with closely spaced tees off your primary loop, the pressure differential created by the primary pump will not "see" any secondary piping.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
0
Comments
-
Primary Secondary pump sizing
What is the best way to size a primary pump. I am looking a the tekmar application #262-2 and I would like to know how to size the P1 pump. I have sized P1 for the total system load in the past and have used circs to zone with and what happend is the P1 pump winds up raising the zone flow checks. tekmar drawing is at. http://www.tekmarcontrols.com/acrobat/a262.pdf
Bill0 -
wrong drawing?
Unless I'm looking at the wrong drawing, 262-2 doesn't have any zone circs.
Mark0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements