long runs with monoflo tees?

d henry
Member Posts: 1
i just completed sweating a 1 zone loop of five radiators. one of the radiators was a bit out of the way, so i put in two 12' foot runs, with a monoflo tee on the feed and return (1 x 3/4)
has anyone done this? will it work? or have i probably plumbed a radiator that won't get hot?
has anyone done this? will it work? or have i probably plumbed a radiator that won't get hot?
0
Comments
-
Sure using two tees is what you can do on down feeds, long runs and tough base board runs . The second tee increases the pressure drop more then one tee does . The pressure drop is what moves the btu's into the radiation. It should work with-in reason as long as the risers are not too long and that you did not leave any air traps to block the flow...0 -
Monoflo tees...
If you have trouble eliminating the air from this setup, you may have to cut in a purge valve set on the return from the heating element and purge it out as a separate zone off of the main.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 939 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements