long runs with monoflo tees?

d henry
d henry Member Posts: 1
i just completed sweating a 1 zone loop of five radiators. one of the radiators was a bit out of the way, so i put in two 12' foot runs, with a monoflo tee on the feed and return (1 x 3/4)

has anyone done this? will it work? or have i probably plumbed a radiator that won't get hot?

Comments

  • Big Ed
    Big Ed Member Posts: 1,117


    Sure using two tees is what you can do on down feeds, long runs and tough base board runs . The second tee increases the pressure drop more then one tee does . The pressure drop is what moves the btu's into the radiation. It should work with-in reason as long as the risers are not too long and that you did not leave any air traps to block the flow...
  • jim bannister
    jim bannister Member Posts: 20
    Monoflo tees...

    If you have trouble eliminating the air from this setup, you may have to cut in a purge valve set on the return from the heating element and purge it out as a separate zone off of the main.