American Standard service problem SE

Steve Ebels
Steve Ebels Member Posts: 904
I'm stumped. Never had this happen or heard of it. New American Standard AUX model furnace (90% single stage). It's showing an error code of 5 flashes which means that there is a flame sensed when none is present. The problem is that I can't get the furnace out of the lock out mode and get it to retry for me. You're supposed to cycle the power on/off on/off within 30 seconds to reset it. It doesn't happen.

Got any thoughts??

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=175&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>

Comments

  • Mark Eatherton1
    Mark Eatherton1 Member Posts: 2,542
    Reversed polarity?

    Just a thought. The five flashes rings a bell.

    ME

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Steve Ebels
    Steve Ebels Member Posts: 904
    Nope

    Polarity is OK. Checked it all the way back to the electrical panel. It's got to be some kind of a ground fault because that's how the flame sensor works. Current to ground. I'm at a loss on the failure to reset when you kill the power.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • ed wallace
    ed wallace Member Posts: 1,613
    error code

    could be a problem with circuit board or hot surface igniter call the local distributer for help
  • Floyd
    Floyd Member Posts: 429
    Is the ignitor touching the burner?

    I agree, sounds like a bad board or ignitor.
  • tombig
    tombig Member Posts: 291


    Could be a ground fault. See if you have any potential from equipment case to true earth ground. Maybe they had some yahoo electrician in there over the summer.
  • This content has been removed.
  • Steve Ebels
    Steve Ebels Member Posts: 904
    David

    And everyone, thanks for the responses. FYI we wound up replacing the circuit board for an immediate fix. I'm still bugged and puzzled though. Bugged that I don't know what caused the board to fail, (maybe it was just a dead board) and puzzled that it would not reset.(maybe that's just the way they are made)

    Anyway thanks

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • ed wallace
    ed wallace Member Posts: 1,613
    problems

    serviced an american standard 90% furnace last year
    system was in 2 weeks igniter failed replaced igniter
    3 weeks later board failed supply house replaced both
    at no charge the board sends variable voltage to
    igniter believe its anywhere from 32volts to 72 volts
    you should talk to the supply house might warrenty
    the board
  • ed wallace
    ed wallace Member Posts: 1,613
    problems

    serviced an american standard 90% furnace last year
    system was in 2 weeks igniter failed replaced igniter
    3 weeks later board failed supply house replaced both
    at no charge the board sends variable voltage to
    igniter believe its anywhere from 32volts to 72 volts
    you should talk to the supply house might warrenty
    the board