A three zone hot water system using Automag DC solenoid valves...developed this problem after a lightning storm: Relay in Aquastat being called by zone terminal board, with NO call from t-stats. It appears the diodes for the valve solenoids, only block AC to the valves. But ANY zone should call the circulator/boiler. Anybody got a schematic for the diodes? I understand why they do DC( to remove AC hum), and that the valves, when energized, are closed. They drop out to open. NOBODY around here has a clue about Automag. Can someone help. Thanks, Robert
0
Comments
-
Hi Rob, Try giving Automag a call at 1 800 451 2002 ask for Jim Specht or Ed.One of them should be able to answer your question.
Your friend in the industry,
Alan R. Mercurio
www.oiltechtalk.com0 -
Automags
are so simple they appear complex. Are the stats original 3 wire or 2 wire with a relay? You can easily test the diode if it doesn't look trashed by the lighting, should pass ohm check in one direction only. I wonder, did you isolate each stat one at a time? I think you might have a bad stat.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements