I bad install .
Joe Grosso
Joe Grosso Member Posts: 307
On my home tonight I stopped by one of my customers home to meet his neighbor.He had a WM gold oil boiler installed with a tankless coil and kept complaining about not enough dhw.By the way a 3 section boiler,no flow resictor and a hand mixer left from the old boiler.I know I may sometimes get on some of you that are plumbers about heating installs, but this one is from one of the biggest in my area.Going to repipe it and add a aqua booster to help out the dhw.Yes I did try to upgrade to a indirect but not always get that sale.Will post the job when done.By the way this job was installed only 6 months ago.
  • Paul_6
    Paul_6 Member Posts: 88
    I can't tell
    did this guy take the time to move the pump to the supply and still pump towards the expansion tank? Paul.
  • ed wallace
    ed wallace Member Posts: 1,612
    bad install
    it looks like there was some soot proplems from the sooting on the jaccket and did he realy set up circ to pump toward expansion tank ?
  • Joe Grosso
    Yes he did
    The circulator is puping right at the expansion tank.Do you think that these boys need to go back to 101 hydronic school.
  • todd s
    todd s Member Posts: 212
    Circ location
    I see this all the time. Weil had the right idea, they put the packaged circs right on top. They should have made the bx longer and put a big orange sticker on it that shows how the rest of the system should be piped.
  • J.C.A.
    J.C.A. Member Posts: 349
    Todd.
    I think they did that to save on the tie strap or bolt that they started with that held it to the pallet .
    Pennies count !
  • todd s
    Burner
    What about the burner problem they were having? I know you will straighten that out also.
  • jim f
    jim f Member Posts: 182
    looks like the problem........
    screwdriver in the control again.....
    this guy must have a lot of screwdrivers if he leaves them on every job!!!.........
    lol..jim f.
  • Theyre heart was in the right place
    A LWCO , the relief piped to the floor , a mixer for the coil ( its even broken-in ) , up on blocks - that baby is a work of art . Now if they only had a level and read a book or 2 on piping techniques ....
  • eleft(retired)
    eleft(retired) Member Posts: 98
    sad
    I notice the aquastat cover is under the pie dish with the cookie tin in it.
    Yeah..there are problems!
    I wonder what the 7/8 wrench is used for, propane bottle??
    al
  • mp1969
    mp1969 Member Posts: 225
    Flow restrictor
    Doesn't this application require a 3 gpm flow restictor?
    How many homes today can get by with 3 gpm of domestic hotwater? The soot around the fire box indicates very questionable combustion. The oil lines laying exposed for foot traffic are not a real good idea either. No wonder you are questioning this install, it is very sad!
    MP 1969