Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Need Tek Mar help
Wayco Wayne
Member Posts: 615
I had a job just land in my lap where I have to straighten out a homeowner installed radiant floor problem. I need a variable circ control for injection with boiler return water control to keep return above 130, (cast iron Burnham). I have a Tekmar 356 sitting on my desk but the boiler sensor in the Aplication diagram has the boiler sensor on the supply. Do I need another controller or can the 356 work for my app. Thanks for your help in advance.
0
Comments
-
tekmar
w,
hope this helps
al0 -
optional return sensor
looks like you just need the (optional boiler return) sensor
Mark0 -
Thanks guys
I finally got to the literature I needed.(D356) The boiler sensor can go on the Supply or the Return. All systems go.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements