45 year old sectional steam boiler
Chuck_7
Chuck_7 Member Posts: 71
I am looking at a 45 year old atmospheric 10 section cast iron steam boiler (Weil McClain).
Looks like it is in OK condition. It does not look like there is much or any water loss. Maintenance has been minimal.
Can I expect the boiler to last much longer??
    Steamhead Member Posts: 18,211
    Boilers last for decades
    if properly maintained. But something that old is probably about 60% efficient (AFUE) if that. I'd consider replacing it on that basis- a new steam boiler will have an AFUE (annual fuel utilization efficiency) of 80-84%. With constantly rising fuel prices this makes sense.
    But since it's in such good shape, you should be able to replace it at your convenience rather than when it gives out.
    You may also consider upgrading the air vents (ESPECIALLY the ones on the steam main) which will allow the steam to distribute faster and reduce the boiler burner's running time. Most steam systems I've seen are not vented properly, and this wastes lots of fuel.
    Go to the Find a Contractor page of this site and follow the directions to locate a good steam man near you. If you're in the Baltimore area, just e-mail me!
    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Oil & Gas Burner Service
    Consulting