Estimating Fuel Cost for Heated Driveway
Tom Anderson
Member Posts: 40
Have heated slab in northen Vermont.... and I have been requested to estimate annual fuel costs.
Looking for guidance on appropriate methodology. I have both degree day data and bin hour data available.
Installing contractor has provided the following information:
Square feet of heated slab
6" concrete
2 inches rigid foam underneath
Design outside air temp
Design Btuh for entire slab
50% glycol solution
Heating runs continually when outside air is below 32F. Intent of heating is snowmelt for safety reasons.
Wondering if I could use degree days, working out the Btu per degree for the entire slab. Or use bin method. Or, is there another acceptable method to use?
This type of heating estimate is a new one for me and appreciate any assistance.
Looking for guidance on appropriate methodology. I have both degree day data and bin hour data available.
Installing contractor has provided the following information:
Square feet of heated slab
6" concrete
2 inches rigid foam underneath
Design outside air temp
Design Btuh for entire slab
50% glycol solution
Heating runs continually when outside air is below 32F. Intent of heating is snowmelt for safety reasons.
Wondering if I could use degree days, working out the Btu per degree for the entire slab. Or use bin method. Or, is there another acceptable method to use?
This type of heating estimate is a new one for me and appreciate any assistance.
0
Comments
-
Fuel Cost
What is your heat source? Your BTU's per sqft should be minimum of 110. I know that Viessmann has developed a software program for fuel consumption comparisons that they use when quoting on commercial jobs. I would try to contact them.0 -
ASHRAE
Go to ASHRAE Applications Handbook, Chapter 49. for a complete method.
Have had clients request similar information, which we provided, but with some type of caveat stating weather data and energy costs are unpredictable and as such calculation is provided as information only. The user or any third party shall hold provider of information harmless for any reliance on said estimate.
The last thing anyone needs is to provide an estimate of energy consumption then have an extreme winter with rising oil prices...some clients will try to make others responsible for things which are out of our control . like an excessive fuel bill.
RB
0 -
Results
RB: Thank you very much. You saved my butt.
My results were as follows, for northern Vermont:
Asssuming 80% boiler efficiency; heating runs constant below 32F ambient; 2" rigid insul undeneath,
Oil, 1.9 Gallons per square foot per year
Wood chip fuel, 50% moisture, .033 tons per square foot per year.
Application is at the state capitol, where a central wood fired boiler plant heats the capitol campus.
Thanks again!
Tom Anderson
0 -
No problem
been through a few mine fields...some you just have to avoid.
RB0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements