one tank-two units

Bill NTSG
Bill NTSG Member Posts: 321
The check valves require a good amount of vacuum to open. They offer resistance to flow. Some of the spring ball type are worse. I have removed some problem ones and reduced the vacuum gauge reading at the pump by 3 or 4 inches or more. If you can get away with out them by all means , DO.

Comments

  • spl
    spl Member Posts: 1


    one tank - 15' away from two units - tank bottom 12" below units - units firing 1.25 and 1.0 - mini pumps

    Q? best way to supply both units without problems of air, etc.
  • John@Reliable
    John@Reliable Member Posts: 379
    Best way?

    You should be able to run one 3/8" supply line close to units and tee off that line.Use flare fittings and flare firomatics. The amount of oil you are using will be handled with this set-up Hope this helps!
  • spl_2
    spl_2 Member Posts: 7
    one line--two units

    Someone told me today that you could use one supply line, tee off, and use one return line, tee off. I was always concerned with one unit running, the return oil would pressurize the other pump's return, as well as return to tank. I am not sure what effect this will have the other pump, and if a hazard is created.
  • JIM F.
    JIM F. Member Posts: 82


    I RUN 1/2 LINE EVERYTIME POSSIBLE USING SEPERATE FILTERSAT TANK ALSO WITH MORE THAN 1 UNITS I PUT IN-LINE CHECK VALVES
  • No need to run return lines

    with a tank that close to the burners . We use 3/8 copper to a filter near the burners and tee it after the filter . Having a filer right at the tank is a good idea also .
  • Floyd
    Floyd Member Posts: 429
    TIGER LOOP!!!!!

    Will solve all your problems!!!!!!
    Run one pipe to one of the units mount the Tiger Loop on that unit and pipe to the second unit.
    No air, no primeing, just a lot less headaches for about 125.00

    Can't beat it!!!

    Floyd
  • Bill NTSG
    Bill NTSG Member Posts: 321
    Seperate lines

    I like to tee off at the tank , right after the filter and run a seperate line to each burner. Single pipe system should be fine. The only time the oil will be below the burner is when the tank is down to a 1/4 tank, right ?
  • spl_2
    spl_2 Member Posts: 7
    tee at tank

    Yes, I like this idea, and it is better than coming off the top. The fact that the oil will be below the tank only when the tank is at 1/4 is not a big deal, if all flares are tight. Mobile home furnaces are always above the supply tank with one line systems, and if all fittings are tight, there is not any problem.
  • J.C.A.
    J.C.A. Member Posts: 349
    2 burners 1 tank.....

    I'd go with what Bill Nye"not the science guy"says , and by ALL MEANS avoid putting a check valve in the line as suggested by Jim F . Check valves in an oil line are a HUGE NO-NO !
    Flared fittings only and quality filter will make your burners happy for their lifetime . Chris
  • Earthfire
    Earthfire Member Posts: 543
    I disagree

    Check valves are not a no-no in oil lines . In fact if the oil pump is higher then about 3 ft. then the tank bottom I always install one . And if Memory serves me right the pump manufacturers specify a checkvalve if the lift is over 8ft. + - . The check valve are specificly designed for use in oil lines with their unique vacumn requirements. one example is a " HOLD-TITE " 3/8 x 3/8 flare model# 105HCV or 1/2 x1/2 flare mod.# 205 HCV. Chances of getting one at the plumbing supply are low .You will probable need to go to a Mechanical supply house like Johnstone, Sid Harvey , R. E. Michael among others They keep them and other brands on the shelf. A "water" check valve will only cause problems.
  • spl_2
    spl_2 Member Posts: 7
    check valves

    Isn't it true that check valves in marginal vacuum (sp?) conditions can cause cavitation, and then loss of prime?
  • JIM F.
    JIM F. Member Posts: 82
    osv valves

    up and coming more and more with inspectors are o.s.v. valves if taking feed off bottom of tank.(anti-siphon valves.) here is a set up we did. notice the hole in the top.. using a paper clip or piece of 14ga wire this diaprahm need to be manually open while bleeding. sorry in this picture the are installed upside down. they should be installed with hole facing down.
  • spl_2
    spl_2 Member Posts: 7
    osv's on pump?

    > up and coming more and more with inspectors are

    > o.s.v. valves if taking feed off bottom of

    > tank.(anti-siphon valves.) here is a set up we

    > did. notice the hole in the top.. using a paper

    > clip or piece of 14ga wire this diaprahm need to

    > be manually open while bleeding. sorry in this

    > picture the are installed upside down. they

    > should be installed with hole facing down.



  • spl_2
    spl_2 Member Posts: 7
    osv's on pump?

    I was taught to put osv units hard piped to fuel units because if installed near tank, oil between fuel unit and osv in tank area can expand and cause a lot of pressure on pump seals. If put on pump, then any expansion would bleed back to tank.

    Am I mistaken or is the osv's main purpose to guard against seal failure and gravity feed, or any leak in general? Thanks in advance.
  • todd s
    todd s Member Posts: 212
    two tanks

    Jim you do very neat work and I'm not picking on you but I hope there are valves directly under each tank. This could be a major problem if: settling occurs and iron pipes start to leak or if either tank needed to be shuttoff for service. What I like to do when doing the tuneup is to shut off both tanks then check for flow out of each. You'd be surprised how often one tank has a clog in the bottom.
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    Jimmy

    ya gotta put the filters before the OSV, so they stay clean.Smart move in installing them! I would use 1/2" copper between the tanks, bent in a curve or some such, so there will not be a stressed joint from tank movement..imagine if one of those 3/8 fitting went *dink!* :)

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    Bill is right

    a check valve has no place in a properly engineered oil delivery system.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • JIM F.
    JIM F. Member Posts: 82
    filters and osv's

    just checked out webster site.learn something every day, i set it up this way assuming that osv should be first to prevent a leak any where in line(filter leak,line leak pump leak, etc.) thanks bob
    and scott yes there are 1/2 in-line ips fire valves on the bottom facing the wall.
    jim f.