Cold Radiator
Dave_23
Member Posts: 190
Please help. I have one radiator in my home that won't heat consistently.
Details:
House: 2100 sq ft 3 br 2 1/2 bath, 14 radiators.
System: Two pipe steam
Boiler: Weil McClain 150,000 BTU
Cold radiator location: 2nd floor bedroom, NOT farthest from boiler.
Symptoms:
1. Veritical inlet/riser pipe at radiator heats up to shutoff valve (too hot to touch). However, radiator won't heat.
2. Shutoff valve fully open
3. Radiator in question heats fine on first heating cycle of season, then no longer heats on subsequent cycles.
4. Other radiators in house work fine.
5. No water hammer.
6. I TEMPORARILY installed a 1A adjustable vent on the radiator for test purposes. Radiator still won't heat. Inlet pipe gets hot though. Plenty of air rushes from the vent upon boiler firing.
Please help? Any other diagnostic tricks I might use to identify the problem?
Details:
House: 2100 sq ft 3 br 2 1/2 bath, 14 radiators.
System: Two pipe steam
Boiler: Weil McClain 150,000 BTU
Cold radiator location: 2nd floor bedroom, NOT farthest from boiler.
Symptoms:
1. Veritical inlet/riser pipe at radiator heats up to shutoff valve (too hot to touch). However, radiator won't heat.
2. Shutoff valve fully open
3. Radiator in question heats fine on first heating cycle of season, then no longer heats on subsequent cycles.
4. Other radiators in house work fine.
5. No water hammer.
6. I TEMPORARILY installed a 1A adjustable vent on the radiator for test purposes. Radiator still won't heat. Inlet pipe gets hot though. Plenty of air rushes from the vent upon boiler firing.
Please help? Any other diagnostic tricks I might use to identify the problem?
0
Comments
-
cold rad
Does the radiator have a trap at the outlet?0 -
Cold rad
No it doesn't. In fact there are about three rads in my system (again, two pipe) that don't have traps. Not sure why. Thanks, I'm a rookie on this subject.
0 -
Are those three original,
Or are they newer piping? I'm trying to figure out what the system started out as...
Noel0 -
brainstorm ?
Rad valve is open, how do you know ? If it were broken just right it could act as a check valve, it would let in steam, that would condensate to water and then the water could not get back down, Trapped there not allowing in steam cold rad. all summer it leaks down and then a one time fill of steam fills up with water and no heat. bigugh0 -
It's probably Vapor
Check your e-mail, Dave- I didn't realize this was on the Wall too!
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
cold rad
Trace the outlet pipe and tell us where it goes.0 -
Cold Rad
If I had to guess, it looks like someone removed the traps and replaced them with short nipples and unions. All rads except the one that won't heat appear to be original (they all work very well, except for the one that won't heat)
I've confirmed that the valve on the rad in question is not broken, opens all the way and doesn't leak.0 -
Could be an orifice system
Might be running on too high a pressure.Retired and loving it.0 -
Could be an orifice system
Normally, would a system consist of orifice equipped rads and trap equipped rads. Or is it one or the other exclusively?0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements