One of my regular general contractors wants us to do a small job; heating in 3 rooms (family room, bedroom and dining room). I though about installing a Polaris water heater for combined heating and domestic.

Heating: Turn the Polaris all the way up, double-walled heat exchanger, 3 radiators.

Domestic: Tempering valve set at 120*.

Has anyone ever done this?

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>

Comments

  • Bill Clinton
    Bill Clinton Member Posts: 75
    ya cum ta du rite plase

    Hell, Allen, I usta be known as da Polaris Kid. What you propose is doable: Don't know if it is a good idea, but it can be done. I'd size the hell out of that double wall and use a commercial polaris with 180 degree thermostat just in case I needed it. Then I'd size the radiators for no more than 140 degrees. Voila monsewer!

    Bill
  • You bought so many

    of them, they manufactured a "Bill Clinton Edition"; they had it bulge in the middle and called it "extended capacity". :>)

    Thanks for the Polaris info.; I'll follow up on it.

    All the best,

    Alan

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Dana Zaichkin
    Dana Zaichkin Member Posts: 29
    Polaris vs Phase III

    Greetings Alan - I was wondering why you would choose a Polaris for use as a combi unit vs a Phase III /Triangle Tube direct fired unit? Did you have a bad experience with the HMPG you installed?

    Best Regards

    Dana
  • hr
    hr Member Posts: 6,106
    Might be the long way around

    If your radiators require 130 or hotter water to get the output to meet the heat load? It may be better to use a small boiler with an indirect tank for DHW. Running a Polaris above 130 defeats the point of using a condensing sourse, sort of.

    I have done a hand full of Polaris with a small flat plate hx. I don't count on much more than 120 degrees at the B side however, with the Polaris cranked to 140 range. Works fine for a small floor warming application, might be a streech for a radiator system however.

    There are a number of premade combo units out there Burnham Minuteman, I believe. Teledyne Laars has a couple combo options. Both fit in small spaces. the weak side ids the fairly small DHW capacity.

    I am going to try a Slant Fin wall hung Prodigy soon for an application like this. Just depends on the heat and dhw needs.

    The boiler approch would handle a radiator temperature better, perhaps.

    hot rod

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Dana and hr

    Thanks for your input.

    Yes, we'd have to forego (sp?) condensing and your probably right about the seconday side of the HX: it would be difficult to get a high enough temperature for the radiators.

    And yes, maybe a Triangle Tube, Minuteman or Baxi boiler would be better.

    We installed a Minuteman about 15 years ago; must've been 1st generation. It had so many problems, I've never forgotten about it. Burnham came though and sent us another one, air freight - prepaid. I was amazed.

    All the best,

    Alan

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Dana Zaichkin_2
    Dana Zaichkin_2 Member Posts: 36
    Hi Alan

    I think you must have installed at least one of every radiant heat source out there - If I recall correctly didn't you even post a photo some time back of a residential reactor being installed?

    Had an inspection scheduled this am for framing/plumbing for our "project". I got to the site and the PUD had the power shut down to the area - including the community well. Fortunately, the power was back up in time to get the DWV filled before the inspector arrived.

    Best Regards
    Dana
This discussion has been closed.