Noisy New Boiler
Jim Serdy
Member Posts: 1
Gents,
We are an 18 unit condominium building with a two pipe steam
heating system. The old boiler gave out two years ago and we replaced it with an 8 section Burnham wet base boiler and a powerflame dual fuelburner.
The resident above the boiler room complained that the new boiler made much more noise than the previous one.
We hired a sound engineer who took measurements. We then erected a suspended ceiling and isolation wall. We installed a blanket in the refractory and back draft damper, downfired the boiler.
New measurements were taken that showed 25% reduction in noise but the resident is still not satisfied.
We have heard of installing a muffler on the flue. Do you
recommend doing this? and who is (are) the manufacturers?
Thank you,
Jim
Thank you,
Jim
Noise
> Gents, We are an 18 unit condominium building
> with a two pipe steam heating system. The old
> The resident above
> We
> boiler.
> We have heard of
> you recommend doing this? and who is (are) the
> manufacturers?
> Thank you,
> Jim
noise
Sound like to me you guys have gone above and beyond for this lady.Maybe cheaper to offer her a condominium further
away from the boiler room.No then she will complain she no longer has warm floors.Blah,blah,blah.Good Luck!0 -
Loud Burner
Sounds like you have done more than I would.If old burner was running @1725rpm motor and new one is 3450rpm you will get more sound of air,burners use alot of air.I once had to put a 12" plug instead of damper in a flue pipe to keep the nuns in a convent happy! Noise went away along with some efficiency. P.S. Boiler was a 9 section Burnham. Hope this helps0 -
noise
Where exactly is the noise coming from? Chimney noise or burner noise? Altho this is not my original idea I have heard of filling up the chimney base with sand as a way to reduce noise. It will reduce the echo of exhaust in the chimney so I have been told. Let us know your final solution.0 -
How does the flue run. If it runs thru a chase adjacent to the subject unit, did you check for openings event tiny ones. Sound can be transmitted thru any opening. Seal the chase and apply sound proofing and I bet you will help your problem. I have seen several noisy boilers where this helps. Installing a class A flue in place of Type B will help in gas fired systems. Uncertain if you are gas fired or oil.0
- 86.9K THE MAIN WALL
- 57 Biomass
- 109 Chimneys & Flues
- 5.7K Gas Heating
- 105 Geothermal
- 70 Pipe Deterioration
- 974 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 44 Industry Classes
