Oversized Steam Boiler

PG
PG Member Posts: 128
I'm trying to figure out how to stop water hammer in a two pipe steam system. All the traps have just been replaced. Boiler is oversized, and brand new......so it is staying. The boiler is a Weil McLain LGB 10W/SN. Rated for 2,963 sq. ft. of steam. Also 711 MBH. Can someone refresh me on MBH......cant' remember what it stands for, or how to use it. Read somwhere that installing a selonoid valve (spell ck!) could be installed to help this problem. Just can't seem to remember where or how to install it? Any suggestions or help would be greatly appreciated! Thanks, Patrick Giroux Grosse Pointe Park, MI.

Comments

  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    same old story

    how oversized is it? How much EDR actually exists? I would take a close look at the piping around the boiler..it also may have been installed in error..

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Steamhead
    Steamhead Member Posts: 17,352
    An oversized boiler

    may cause water hammer- then again, it might not. How "oversized" is the boiler and have you been able to tell exactly where the banging is coming from?

    Also, what variety of two-pipe steam is this? Is it a "vapor" system? Have you located any manufacturers' names on the various components of the system, including any strange-looking things near the boiler or out at the end of the mains?

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Boilerpro
    Boilerpro Member Posts: 410
    Downfire it

    I believe LGB 's come with two stage gas valves whether or not it has two stage controls. Just disconnect the wire to the high stage terminal on the gas valve. The other Boiler guy at my church did this to our church boiler after I did a heat load calc and shut off rads to get the radiation to match the load. We went through last winter at low (50%) fire just fine on this three zone system.