How do I know if garage sale radiators are good?
Nancy Engel
Member Posts: 2
Hi, our home is heated with steam radiators. I bought some as "back ups" at a garage sale. How do I know if these radiators, that are now sitting in my garage, are in working order or not?
Thanks for your help!
Thanks for your help!
0
Comments
-
If by "working order" you mean "not cracked" then you will need to pressure test them.
This could be done with air or water. Any holes would have to be plugged and then you would pressurize the radiator through one of them.
The method you choose for pressurizing will determine what type of adapter you will need.
For a water test you would need a bushing with a hose bib to attach to a hose.
For air you would need a bushing and a connector for a compressor.
If you use an air compressor, DO NOT over pressurize the radiator!!!!!!!
Hope this helps!!
Mark H
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
safety first
Much safer to test with water ! (it doesn't compress like air does)
0 -
Yard sale
Why would you need back-ups?,they must be sized to work right on your system.But then again I can't pass up a good yard sale bargain!Test with water and if you do ever need then make sure they are the right size for job.0 -
Testing
If you didn't get the original valves and angle unions with the rads, you'll probably have to remove the bushings and other half of the union connections. Unless you find the valves/angles by the same mfgr. you're unlikely to get a tight connection. They can be REALLY tight. Use a big wrench and a breaking bar.
Typical household water pressure can sometimes cause very slow, weeping leaks BETWEEN sections on rads assembled with push nipples. You can easily tell if they use push nipples as there will be threaded rods running horizontally through the rad. Hot water systems operate under much lower pressure and this type of leak is unlikely to recur.0 -
air test
to test the radiator for leaks fill with water and pressurise to about 30 to 40 psi with WATER, no more . Your heating system should never see pressures that high. If you use air to pressure test if a crack lets go the resulting schrapnel flying thru the air could very easily be a fatal missle, not to mention a hole in the wall. With water behind that piece of metal it won't fly. For safety sake DO NOT USE AIR use water.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements