near-boiler piping on gravity conversion
Mark J Strawcutter
Member Posts: 625
My understanding is that reducing the size of near-boiler piping on a gravity conversion to forced circulation is to provide enough pressure drop to satisfy the head requirements of the circulator.
Since this is usually a function of pipe size and length, and since such a short lenght of pipe is involved, I also suspect that the rule-of-thumb for "half the size of the mains then drop one size" intentionally produces a much smaller pipe size than would "normally" be used.
If my assumptions/understanding are/is indeed correct, would it not also be possible to achieve the same goal with a [partially closed] balancing valve in larger piping?
Mark
Since this is usually a function of pipe size and length, and since such a short lenght of pipe is involved, I also suspect that the rule-of-thumb for "half the size of the mains then drop one size" intentionally produces a much smaller pipe size than would "normally" be used.
If my assumptions/understanding are/is indeed correct, would it not also be possible to achieve the same goal with a [partially closed] balancing valve in larger piping?
Mark
0
Comments
-
near boiler piping
I did something like that before on a boiler/gravity conv. It was only after that I read "How come" Dan has an excerpt on the heating Q&A section of this website.
The ball valve closing would work, but why spend the xtra money on bigger pipes and valves, unless its already done... kpc0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements