Snowmelting questions
Bob Murray
Member Posts: 20
My fellow wetheads...
I am about to install my very first snowmelting system. I have a couple questions if you don't mind.
I will be heating an area approx. 1600 sq. ft. (40 x 40). 140 deg supply temp, 8"c-c, 8-300" loops 5/8" pex.
This will be going under asphalt. I was told to put a layer of sand 2-3", then bfb bubble insulation, 6" flat wire mesh, tubing, another 2-3" of sand, then asphalt (with cold water flowing through tubing during and 8 hours after pour).
Questions:
Is the sand a good enough base just under the asphalt? I was thinking of stone dust as the top layer. It would pack real nice for the asphalt.
Is stone dust OK packed around pex? Is it fine enough to not do any damage to the tubing during expansion and contraction?
Is their another preffered way to do this? Please don't tell me concrete. The job WILL be asphalt.
Thanks for any input.
Bob Murray
Yankee P+H
Tuftonboro, NH
I am about to install my very first snowmelting system. I have a couple questions if you don't mind.
I will be heating an area approx. 1600 sq. ft. (40 x 40). 140 deg supply temp, 8"c-c, 8-300" loops 5/8" pex.
This will be going under asphalt. I was told to put a layer of sand 2-3", then bfb bubble insulation, 6" flat wire mesh, tubing, another 2-3" of sand, then asphalt (with cold water flowing through tubing during and 8 hours after pour).
Questions:
Is the sand a good enough base just under the asphalt? I was thinking of stone dust as the top layer. It would pack real nice for the asphalt.
Is stone dust OK packed around pex? Is it fine enough to not do any damage to the tubing during expansion and contraction?
Is their another preffered way to do this? Please don't tell me concrete. The job WILL be asphalt.
Thanks for any input.
Bob Murray
Yankee P+H
Tuftonboro, NH
0
Comments
-
Sorry about the screw up.
ME0 -
Check this out Bob...
I found it with a Google search using the words 'asphalt snowmelt'. There are others there too.
Make sure you get ALL the water out of the tubes prior to inducing rubbing alcohol. Did I say rubbing alcohol???
NEVAH MIND... I must have been thinking geo-thermal...
http://www.pmmag.com/CDA/ArticleInformation/features/BNP__Features__Item/0,2379,4137,00.html
ME
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
bob
I'm sure some will disagree with me and it does depend on the agrigate in the asphalt but I have done this without sand to protect the tube. We put down 6" x 6" flay wire mesh tied the tubes to the mesh and the hot asphalt was wheel barrowed and hand tamped over the tubes. We did run cold water through the tubes during the asphalt placement. However we did a little experiment with a piece of tube in the wheel barrow. We put hot asphalt 6" over the tube with no water and the oxygen barrier was not even degraded. I would still feel safer with cold water flowing. Anyway I wouldn't deminish the heat transfer rate and add this extra step of imbedding the tube in sand. I can tell you we did this job last fall and in Buffalo NY we received 3' of snow in a day and this baby melted like a champ. I swear it melted faster than the concrete jobs we've done. We used 3/4" tube on 300' loops. Good luck. That's just my experience.0 -
Troy,Stupid ? here
While circulating the cold H2O do you leave the draw off open on the returns of the loops?
cheese0 -
Thanks for your responses guys...All information recieved so far has helped alot and is very valuable. Anyone else care to put their 2 cents in?
Bob0 -
cheese
> While circulating the cold H2O do you leave the
> draw off open on the returns of the
> loops?
>
> cheese
I
'm not sure what you mean. We did let the water run freely out of the return header if that is the question. The supply was fed with a garden hose and had continuous cold water feeding it during the pour. My point was even without cold water in the tube during our little test the tube did not distort.0 -
An article from IPEX
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements