Are you familiar with R7426C "Flextronics" or "miconik 200"
Are difficult are these to set up for a typical AHU with heating coil and economizer dampers fixed minimum OSA with cascade control of discharge air temperature?
eric
eric
R7426C1020 &1038
The R7426C1020 is a commercial electronic controller for heating, cooling & damper systems. It has 3 analog and 1 relay outputs, a realtime clock and is 7 day programmable. The R7426C1038 has 3 analog outputs only, and is time independent. Outputs are 2-10 volts(dc). Each require one main sensor, PT1000 or 20K ohm (not included). Both provide P+I control with adjustable time, summer/winter reset, freeze protection & cascade control for discharge applications. These are restricted to Authorized Honeywell Systems Wholesalers, and you will need to work with them to install and start this product up. Visit the www.honeywell.customer.com website, and follow the prompts to get technical literature. I hope this is helpful to you.0