One-Pipe Steam Piping Questions
Richard Koochagian
Member Posts: 2
I am currently repiping the steam main and risers in my house and have two questions regarding one-pipe steam systems.
1. I have read that I must pipe the steam main vent using a wye or wye trap along with the vent. I have not been able to find a description or diagram of this so that I can pipe the vent propery.
2. Are there any issues with using pipe unions in vertical risers or in a 2 inch horizontal steam main?
Your assistance with eiter of these two topics is appreciated.
1. I have read that I must pipe the steam main vent using a wye or wye trap along with the vent. I have not been able to find a description or diagram of this so that I can pipe the vent propery.
2. Are there any issues with using pipe unions in vertical risers or in a 2 inch horizontal steam main?
Your assistance with eiter of these two topics is appreciated.
0
Comments
-
I've never seen or heard of Having to use.......
a "wye" or "Wye trap" (Is that another name for a strainer?). Anyhow, if properly placed, 12-15" back from the drop and up nice and high on a nipple, a Wye could be nice as it might afford a little extra protection from the abusive, fast-traveling steam. However, we usually use a standard tee, with no problems. I feel that unions (or onions as I like to call 'em)are fine on vertical rises, but should try to be avoided on horizontal runs as they tend to collect and pool some condensate, which can cause snap crackle pop and Some big banging!!!!!! However, if your pitch is good, they really aren't usually an issue. Good luck and welcome to the Steam Club (free lifetime membership fee, but the dues will kill ya!!!!!) You have now begun your study of the artes perditae vaporare calorare(Latin for lost art of steam heating) Keep us posted Pal. Mad Dog
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
steam re pipe
As Mad Dog said, never heard of this fitting. Aside from the quick vent(s) at the end of the mains, pitch all the piping 1" in 20', take off the riser connections on 45*s, don't use 1" pipe on horizontal take offs, insulate the new piping, watch the "A" dimention, install the Hartford Loop PROPERLY, put in drain cocks for flushing purposes,support all piping correctly, etc., etc., etc.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements