Radiant Floor Heating

Options
moose5
moose5 Member Posts: 7
Any experience using 7/8" Durapoly XL 16" on center in the joist space with heat diffusion plates? This system is sold by Radiant Heating Company in Barton ,VT. The house new construction,well insulated,cathedral ceiling,skylights,ceramic tile and solid oak floors. Heat loss calcs.say it will work.Anyone have experienc with 7/8"Durapoly XL ,16" on center,or Radiant Heating Company?

Comments

  • Mike Kraft
    Mike Kraft Member Posts: 406
    Options
    Moose

    Do yourself a favor.Gather more info from other manufacturers/contractors.Floor panel heating/warming is more then stringing pex under the subfloor.

    This company is proposing a 1" tube stapled center of each joist bay to support the load on a design day.The tube is non 02 protected.So all system parts must be non ferrous.They recommend water heaters to supply the system water.Not that theres anything wrong with that :)!!Just depends on the load.

    Check a Long Island CO/RTI,Wirsbo,Roth,Slant Fin,Rehau and so many many more that design in real world conditions and care about what they sell and who they sell to.

    cheese
  • hr
    hr Member Posts: 6,106
    Options
    The tube and fittings

    should have an ASTM F876 and or ASTM 877 listing to meet code in most states.

    There may be aditional DIN standards, NSF, SDR, ICBO, as well as Canadian approvals on the tube.
    Most manufactures will be happy to send you copies of the various listings that their product carry. These are also required by code to be printed on the tube, and fittings.

    Find out what is required in your area.
    It may not be worth gambeling on a product that is not designed or listed to these industry standards. Why risk a problem or code violation with a non listed product.

    hot rod

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Paul Pollets
    Paul Pollets Member Posts: 3,656
    Options
    Calcs?

    Whose calcs show it would work? The design for underfloor joist bay heating should be piped on 8" centers with transfer plates. I'd be using software from a major tubing manufacturer to make sure the design works, and won't need supplemental radiation to meet actual design loads. Don't take it for granted.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"