Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
rare repipe opp
cdennis
Member Posts: 5
have won t&m bid for repipe of 3 story old home with existing 2-pipe cast iron thin tube rads and some cast in wall convectors.Only job spec is all has to be copper lines and risers.have succesfully sold gc and h.o on cont pump with reset...question...2-pipe reverse return, or monoflo tees,or other ideas thanks guys
0
Comments
-
also will have trv's0 -
Use
reverse return with TRV's. Use a pressure bypass differential on the pump and a 3 way or 4 way modulated mix at the boiler. this will easily protect the boiler from thermal shock. I use the Viessmann setup as a matter of course, but tekmar controls work fine.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements