John@Reliable
Member Posts: 379
Steamhead,
What do you think about this,when I install a small steam boiler I always pipe fill so that it will go thru return and hartford loop.I feel this way will always keep these pipes open and clog free. Thanks
What do you think about this,when I install a small steam boiler I always pipe fill so that it will go thru return and hartford loop.I feel this way will always keep these pipes open and clog free. Thanks
0
Comments
-
boiler water feed
it is always best to pipe your water feed thru the return before hartford loop. you do not want to feed directly into any boiler tappings because cold water entering a hot boiler surface could shock boiler. I always install say 1-1/4 x 1/2" tee on return line before rising up to hartford loop. I've seen jobs where installer used a reducing tee instead of elbow right at close nipple in equalizer to connect feed line, this creating water hammer if water was added at time boiler was under pressure. As an added feature i recommend a shut off valve before hartford loop and a 3/4" full port ball upstream to flush return line.0 -
Rick is right
I couldn't have said it better!
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks Rick & Steamhead
This is how I'm doing it,you just explained it better than me Thanks0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 892 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements