Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
2 Tier Baseboard
Eric
Member Posts: 95
On 2 Tier baseboard, circuits normally in parallel?
What are disadvantages or running in series other than lower leaving water temperatures, and slightly reduced output?
What are disadvantages or running in series other than lower leaving water temperatures, and slightly reduced output?
0
Comments
-
series
piping in series will produce a higher pressure drop and may cause flow problems, which may need larger pumps which cost more to supply and operate.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements