2 Tier Baseboard
Eric
Member Posts: 95
On 2 Tier baseboard, circuits normally in parallel?
What are disadvantages or running in series other than lower leaving water temperatures, and slightly reduced output?
What are disadvantages or running in series other than lower leaving water temperatures, and slightly reduced output?
0
Comments
-
series
piping in series will produce a higher pressure drop and may cause flow problems, which may need larger pumps which cost more to supply and operate.0