What is the Heat Loss
frank_2
Member Posts: 6
Can any of you wetheds tell me of the heat loss per/ft. of 1" black steel pipe being used as a radiant loop? None under concrete though, it's surrounded by wood flooring and insulated underside.
0
Comments
-
ifin I
read the Burnham heating helper correctly.. page 46 say.....19btu@100,34btu@120F,61btu@150F,90btu@180,123btu@210F.
I think I am reading that right. Kevin C.0