What is the Heat Loss

frank_2
frank_2 Member Posts: 6
Can any of you wetheds tell me of the heat loss per/ft. of 1" black steel pipe being used as a radiant loop? None under concrete though, it's surrounded by wood flooring and insulated underside.

Comments

  • kevin
    kevin Member Posts: 420
    ifin I

    read the Burnham heating helper correctly.. page 46 say.....19btu@100,34btu@120F,61btu@150F,90btu@180,123btu@210F.