Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
What is the Heat Loss
frank_2
Member Posts: 6
Can any of you wetheds tell me of the heat loss per/ft. of 1" black steel pipe being used as a radiant loop? None under concrete though, it's surrounded by wood flooring and insulated underside.
0
Comments
-
ifin I
read the Burnham heating helper correctly.. page 46 say.....19btu@100,34btu@120F,61btu@150F,90btu@180,123btu@210F.
I think I am reading that right. Kevin C.0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 95 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 890 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements