vaporstat vs pressuretrol
Jeff
Member Posts: 2
I have a one-pipe steam system and am using a pressuretrol Dan's book states that it will do my boiler a true service to replace the p-trol with a vaportstat. the guys at my local plumbing store say to leave the p-stat and that a vaporstat is only used in commercial applications!!!!! Anyway, what model should I use...is there a specific one and can I use one on a millivolt system?
0
Comments
-
Vaporstat
check out www.customer.honeywell.com
Hope this helps
0 -
I think the supply house guys
are confused. Vaporstats belong on heating systems that are designed to operate on less than 1 psi, which would include just about every house in America.Retired and loving it.0 -
Be a little careful
on the honeywell website. I typed in vaporstat and got only one model and the PDF file was only a one page descrtiption that described very little. You still can probably get a choice between 0 to 1 PSI and 0 to 4 PSI with their models. Just make sure the one you get opens on pressure rise like a 404A. Perhaps someone will give the exact model number they currently purchase,0 -
Oh how I wish
we had burners that mimicked the coal fires of old! Perhaps with ribbon burners turned on a slight angle so that as the fire dies down, the heat moves correspondingly closer to the cast iron sections. Gotta fire on full tilt for good light-off, but could quickly modulate back using outdoor reset.
just like banking the coal fires of yester-years?
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Vaporstat model info
Model# L608A1046. This has a single-pole, double-throw mercury switch so it can be used for either open-on-rise or close-on-rise applications. Its range is 0 to 1 PSI. Unfortunately, it ain't cheap.
I generally don't use these on one-pipe systems unless there is a severe overheating problem and all the other factors (firing rate, thermostat anticipator etc) check OK. But on Vapor systems, this control is essential since these systems are designed to run at less than a pound.
Hope this helps.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Vaporstats
There are only six models of this control. They may not be available at all distributors, since they are in the FlameSafeguard catalog, meaning that the distributor will probably be more commercially-oriented. I'll list them below.
L408A1132 SPST break on rise 0 oz/in2 to 16 oz/in2
L408A1157 same 0 psi to 4 psi
L408B1131 SPST make on rise 0 oz/in2 to 16 oz/in2
L408B1149 same 0 psi to 4 psi
L608A1046 SPDT,breakRB,makeRW 0 oz/in2 to 16 oz/in2
on rise
L608A1053 same 0 psi to 4 psi
Enter those numbers in the techlit section of the new webpage and you'll get more info. Thanks for using Honeywell products.0 -
oops!
I'm sorry about the scrambled mess this turned out. I typed a table in, but the gnomes that move the 0's & 1's around mixed it up. Email me if you want any translation.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements