Low Pressure Steam Gauges

Does anyone know where to obtain low pressure steam gauges? I am trying to find one with a range of 0 - 2 psi (or 0 - 3 psi), or one that is in ounces, to use on a commercial steam heating boiler.

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    low pressure gauge

    i found the best selection at www.gaugestore.com. mine is 0-15 ounces, ideal foe steam heating systems. i mounted it on the same pigtail as my vaporstat. if you have no vaporstat, and think your pressure may be higher, ask them how much over-pressure the gauge can stand without permanent dammage. my system cuts in at 3 ounces, and cuts out at 10 ounces.

    be sure to mention that you heard about them on heatinghelp.com--maybe they will advertise here!--nbc
  • Michael Flesher
    Michael Flesher Member Posts: 3
    Low pressure gauge

    Nicholas, what exactly is your brand and model/part no.? I spoke to someone at guagestore.com (Industrial Automation) who told me they do not have anything that low that will work on steam.
    Mike
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    steam gauge

    i got a wika 0-15 oz. gauge, and when it is mounted on the pigtail, or "syphon tube" it is protected from the temperature of the steam. conventional pressure gauges have an "internal syphon", which is convenient for the gauge mfg. as it seems to plug up requiring replacement. the code requires the orig 0-30 psi gauge to remain on the boiler, but it is useless for our purposes.

    if they would advertise here they could sell a lot of gauges!--nbc
  • Michael P. Bourque
    Michael P. Bourque Member Posts: 37


    The gaugestore does sell a low pressure 0-3psi. However you will need to install both a 0-30 and a 0-3 as the 0-30 is required by code.

    Also these gauges cannot take a lot of heat and most are rated at 145 degrees. To remedy this you need to install a pigtail in the gauge port and make sure it is filled with water before putting on the gauges.
  • lovesteamheat
    lovesteamheat Member Posts: 4
    Aha moment with pressure but still???

    I have a 100 year old single pipe system in a large Victorian home (9 radiators) that I have been tweaking with many of the recommendations in 3 of Dan's books. Re-insulated lines, new relief valves, etc and have saved some money and I am now looking at pressure, differential pressuretrol etc.  The pressuretrol sits on a 1/4" x 8" riser and is set to cut in at .5lb and out with a 1lb differential. Great right, wrong I guess, cuz when I put my shiny new pressure gauge on the same riser and boiled er up, guess what no pressure. I ordered a 15LB gauge because that is what was on there and not moving. I can blow about 2lbs pressure into the gauge manually so pretty sure it's fine and there is visible steam pressure coming out of the riser but I get no reading.



    And so the pressure in ounces ???  Is my system operating on ozs of pressure? Is it possible that the differential pressuretrol calibrated in lbs (not ounces) and the 15lb pressure gauge were installed by a numbskull who should have had a pressuretrol calibrated in ounces?



    And??? Do I need a pressuretrol calibrated in ounces?
  • BobC
    BobC Member Posts: 5,491
    If the boiler is matched

    to the connected load it's possible for it to work at almost no pressure. If your sure the pigtail is clear so the pressuretrol and gauge can "see" the boiler pressure and the system is working good, you may have no use for a pressure device on that boiler.



    If the above is true then the pressuretrol is just acting as a safety device, there is no need to calibrate anything. You could use a really low pressure gauge to see whats going on inside that boiler. As long as there is a pigtail between the boiler and the gauge, the gauge does not have to be rated for steam. On my boiler the input of the pigtail is blazing hot but the base of the gauge is just warm.



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • ChrisJ
    ChrisJ Member Posts: 16,122
    Pressure

    Under normal conditions I see around 1oz PSI on my system.  Even with two radiators shut down via TRVs which combined equal 99sqft I've only seen 7oz when it was -3.5F outside.



    I did see the system cycle on pressure @ 1.5 PSI one time and it was after an hour and 20 minutes during a 9 degree recovery.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • flyers03
    flyers03 Member Posts: 14
    I just installed a new pigtail with a tee for my pressuretrol on one side and a new 0-3 psi gauge on the other. My pressuretrol is set at .5 cut in and 1 differential. My question is regarding the new gauge. The needle twitches but never moves from the below zero position. Did I mess up the installation? I attached a picture. This picture was taken 30 minutes in with boiler running. Thanks!
  • jch1
    jch1 Member Posts: 200
    How much water do you need to put into the pigtail?
  • Captain Who
    Captain Who Member Posts: 452
    @flyers03 - Unless all your main vents and radiator vents are hot and closed you won't begin to show any visible pressure on that 0-3psi gauge. Do an overnight setback and get up early before the system starts and observe.
  • flyers03
    flyers03 Member Posts: 14
    @Captain Who I'm sorry I'm kinda new to this. Did I purchase the wrong type of gauge? What do you mean by overnight setback?
  • Captain Who
    Captain Who Member Posts: 452
    edited January 2015
    @flyers03 - ha ha no problem. No your gauge and install looks perfect. If you have a digital thermostat you can program it to do an overnight setback. Mine is set for a setpoint of 61 F from 7:45am to 10pm and 53 F (8 deg setback) from 10pm to 7:45am. If you don't have a digital thermostat you can just do it manually before you retire and when you get up you can put it back up so you can give the system a workout and observe the pressuretrol cutting out out and cutting in on pressure.

    If your pressuretrol has a mercury switch in it, you need to rotate that pigtail 90 deg relative to the rest of the assembly so that it doesn't tip when the heat hits the coil of the pigtail. They haven't made them with mercury switches for some number of years. Open up the case by removing the screw and check. You'll see a glass bulb with mercury in it if you've got one of the old ones.
  • flyers03
    flyers03 Member Posts: 14
    @CaptainWho Thank you. I'll try it tonight. I did run the boiler for about an hour and a half and the gauge remained below zero and the system never cut out. The digital thermostat read 69 degrees when I started and it raised the temp to 73 degrees (which I set it to go). The thermostat shut down the boiler when it hit the temp i set. Could it be that the pressure in my system is really low that the pressuretrol never really comes into play?
  • flyers03
    flyers03 Member Posts: 14
    @Hatterasguy‌ Thank you very much for the input. I am a bit anal so I might just have to go out and get the other gauge. I'm loving steam heat and learning more about maintaining the system.
  • Captain Who
    Captain Who Member Posts: 452
    edited January 2015
    "Could it be that the pressure in my system is really low that the pressuretrol never really comes into play?"

    Yes it could but that'd be a bit unusual for an hour and a half of burn time. Were the radiators hot all the way across so that all the vents should be closed? Unless your boiler is very small relative to the total radiator load you should have seen "something" on that gauge.

    You need to verify that when you do the test tomorrow morning. Check for vents that are leaking steam even though hot and look for any possible steam leaks at pipe joints (much less likely). Do you have to add lots of makeup water to the boiler? That'd probably be the case if you have leaks.
  • flyers03
    flyers03 Member Posts: 14
    edited January 2015
    @CaptainWho after running the system for an hour and a half all 11 radiators were hot all the way across. The vents on the radiators are adjustable so they are not all necessarily closed completely. I also recently updated them all to be sure they are all working. The main vents are both new this season.

    I don't find myself adding water to the boiler often. Should I try completely closing the vents on all the radiators?

    Now that I think of it, I did notice one vent in my back room that was making a whistling noise last night.
  • Captain Who
    Captain Who Member Posts: 452
    "The vents on the radiators are adjustable so they are not all necessarily closed completely."

    That wouldn't cause them to not close if the radiator was heated all the way across. All steam radiator vents close on temperature. Check them tomorrow morning with a mirror. If the vent is hot and the mirror is showing a fog on it from steam, then the vent is not closing as it should.
  • flyers03
    flyers03 Member Posts: 14
    @CaptainWho Will do. Thank you for the direction.
  • flyers03
    flyers03 Member Posts: 14

    flyers03 said:



    If you're anal, like some of us, you now go out and buy another gauge that reads in ounces, with a proper needle valve and snubber............but, there really is no need for it.

    If I wanted to pick up a gauge that reads in ounces, which should I get: 0-10 oz, 0-15 oz?
  • flyers03
    flyers03 Member Posts: 14
    One last question on the gauge. Shouldn't the gauge register 0# prior to start up when the system has been at rest overnight? Or is it acceptable for the needle to be below 0. For example, the boiler was off for 6 hours. Prior to start up, the needle on the new 0-3 psi gauge was far below 0#. Just want to be sure that the gauge isn't faulty and that is normal.
  • Captain Who
    Captain Who Member Posts: 452
    edited January 2015
    @flyers03 - most gauges have a "zero adjust" screw on the back or the front (yours is on the front). It wouldn't be a crazy idea to adjust that so that it registers zero. The zero on yours is ill defined so just raise the needle up until it is just at the bottom of the black bar region. Having said that though, ideally it is more important to calibrate it at the operating pressure if you have a way of doing that. Since you don't have a U-tube manometer or a reference pressure gauge you don't have any way of doing that, so I'd zero it out with the adjustment screw.
    alano9999
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    unscrew the gauge to make sure the water in the pigtail is not slightly out of balance, causing a slight negative pressure. I would be wary of doing any adjustments on the gauge.--NBC
  • flyers03
    flyers03 Member Posts: 14

    unscrew the gauge to make sure the water in the pigtail is not slightly out of balance, causing a slight negative pressure. I would be wary of doing any adjustments on the gauge.--NBC

    Thank you. Should there be a specific amount of water in the pigtail? Do I make sure it's filled to the top of the threading?
  • Captain Who
    Captain Who Member Posts: 452
    edited January 2015
    You couldn't fill it all the way up to the threads if you tried but you only need a few ounces of water in there. I'm not so sure that it is possible for a vacuum to really be there, provided that the pigtail is not clogged. The only other way there could be a slight imbalance would be if there was a lot of water in the pigtail and there was a different temperature in one of the water columns relative to the other. If the pigtail is at an even temperature you can rule that out. I'm assuming that since you just did this installation that you poked a rod through into the boiler to make sure that everything is clear and also that the pigtail is clear?
  • flyers03
    flyers03 Member Posts: 14

    You couldn't fill it all the way up to the threads if you tried but you only need a couple ounces of water in there. I'm assuming that since you just did this installation that you poked a rod through into the boiler to make sure that everything is clear and also that the pigtail is clear?


    Yes I poked a rod through into the boiler to make sure it was clear. There was some blockage in there as I suspect it was never cleaned. The pigtail is new so no issues there. I didn't put any water in the pigtail when i installed it b/c i was under the impression that it would fill with water on it's own. (i guess that was a beginners mistake). Also, the old pigtail didn't seem to have any water in it when i unscrewed it. I mean there was trace amounts of water but nothing to write home about.
  • Captain Who
    Captain Who Member Posts: 452
    Adding water is just a precaution. In my opinion the length of the pigtail and piping below and above it provides heat protection in and of itself.
  • flyers03
    flyers03 Member Posts: 14

    Adding water is just a precaution. In my opinion the length of the pigtail and piping below and above it provides heat protection in and of itself.

    the pigtail itself was extremely hot but the gauge and the pressuretrol did not get hot at all. I figured all was okay. I'll do as you said and check the vents to see if there is a steam leak at one of the radiators. Thank you for all.
  • Captain Who
    Captain Who Member Posts: 452
    Just one more suggestion. If you already know or are pretty sure that one of the vents is leaking (the one you said was whistling when it was hot) AND you have a new one to put in there of the same vent size, it would be a good idea to replace it before the recovery test tomorrow morning.
  • flyers03
    flyers03 Member Posts: 14
    thank you all for your help. As suggested I checked all of the radiator vents for possible leaks and found 1 that had an issue and replaced it. I also inspected all visible pipes and the connects and there doesn't seem to be any visible leaks. That being said, the pressure is still very low but since everything seems to be working great, i'm going to leave well enough alone. The boiler is quiet and the water is the cleanest i've ever seen it (thanks to scout). maybe one day down the road i'll pick up a new gauge that measures oz's instead to get a more accurate reading. Have a great weekend all!
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    The vents whistle on the end of the cycle, when the vacuum begins to draw the air into the system, and usually hiss when the air is being pushed out.
    With good main venting, the radiator vents should become almost completely silent.--NBC