Is there a rule of thumb for the maximum btu output through hardwood floors (slab with sleepers over frame floor),or is the max output drastically different from one type of hardwood to another?
There was an error rendering this rich post.
0
Comments
-
RFH and hardwood
If you look around there are many general guidelines for using hardwood over radiant.
MOST sources will limit the output to around 20BTUH per sq.ft., a surface tremperature in the 78 to 80 deg F area.
You can check the standards area of the RPA website as well as the Hardwood Council site.
Some form of slipsheet should be used between the hardwood and the subfloor - we use 6mil plastic sheeting.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
RFH and hardwood
If you look around there are many general guidelines for using hardwood over radiant.
MOST sources will limit the output to around 20 BTUH per sq.ft., a surface tremperature in the 78 to 80 deg F area.
Constant flow with reset are also wise design choices.
You can check the standards area of the RPA website ( www.radiantpanelassociation.org ) as well as the Hardwood Council site.
Some form of slipsheet should be used between the hardwood and the subfloor - we use 6mil plastic sheeting.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
This site has some information, lots of links.
http://www.woodfloorsonline.com/techtalk/woodwater7.html
John
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements