Piping Injection pumps - Boilerpro
Boilerpro
Member Posts: 410
When installing injection pumps in a vertical run parallel to the injection return piping, what methods do you use to provide some piping give in order to make installation and replacement of the pump easier. If is piped straight in, there is little give in the piping to get the gaskets in place with the pump. I was thinking maybe a linear pipe expansion coupler or maybe a loop of soft copper. Maybe they simply are best installed with some horizontal
offsets to provide the give (like in tekmar's installation instructions)?
Boilerpro
offsets to provide the give (like in tekmar's installation instructions)?
Boilerpro
0
Comments
-
Servicing a circulator
doesn't require the replacemen of the volute. Any wet rotor pump can be completely serviced by removing the powerhead (rotor/stator/impeller assembly) and bolting a new one on the old volute. You can simply remove the 4 screws that hold the motor assembly in place, remove it and replace it with a new one.
Obviously if the volute is the problem, this isn't a solution, but that's a pretty rare occurance.0 -
Consider the flat gaskets
I like these for ease of assembly. They seem to slide in easily, and they don't need to compress much to be leak proof.
hot rod
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
taco freedom flanges
...have built-in ball valves0 -
Servicing a circulator
Unless you are replacing a UFC Injection pump!!! We have had to turn the flange on the adapter a 1/2 or full turn to get the flanges in.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements