Tank not getting equalized

Options

I have 3 tanks from Roth and it is not getting equalized

Thanks

Ketan

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,440

    Need pictures of the piping. When the burner runs it should equalize. It might take some time.

    Mad Dog_2HVACNUTSuperTech
  • 3 tanks properly piped have have 12 flare fittings at the tank For the oil line. You probably have a vacuum leak.
    How were the supply and return fills piped? We’re they only filled pressurized or did someone pump oil over from an old tank.

  • oil was pumped, but the whistle stopped at 17 gallons , the first tank was filled and the oil didn’t pass to the other tanks

    How can I fix the vacuum leak Or how does that happen

    Thanks

  • HVACNUT
    HVACNUT Posts: 7,855

    What's the level in tanks 2 and 3? Are the tanks piped using the Roth kit for multiple tanks? With the kit and single fill, tanks must be filled at a rate of 40-85 GPM.

  • leonz
    leonz Posts: 1,999

    Series parallel connections do not work well unless the feed pipe is in the center of the delivery line and the oil is pushed through at a low speed under low pressure.

    Pumping crude or refined oil like this requires one to think of the tank trains use by Southern Pacific in California when they moved crude oil. they pumped the oil in the last tank car and after it was filled it traveled to the next car and then on and on for the 30 car trains until the last tank car was filled. the tank train was emptied in the same way using inert non-flammable gas to pressurize the last tank car at the refinery to push the crude oil out of the tank train to the tank farm at the refinery.

    The first tank was filled and the air in the other two tanks jumped ship and offered no resistance when the fist tank was filled it indicated the tanks were filled.

    They will have to come back and pump more oil in slowly or have 2 employees come to drop fuel from the bobtail rig by gravity with one person at the bottom connection valve and the other at the filler pipe with along hose.

  • neilc
    neilc Posts: 3,223

    are the whistle vent and fill mixed up outside?

    known to beat dead horses
  • tank 2 and 3 reads 1/4 but the first tanks seems to be full

  • 109A_5
    109A_5 Posts: 4,852

    I can't exactly see where the lines go but I'm guessing the equalizing line has a vacuum break, that breaks the siphon so the equalization stops. Or the air was never purged out if the equalization line. Or if the equalization line is also a return line the return line breaks the siphon.

    Does the red hose go to the floor ?

    image.png

    Not seeing this either.

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,440

    They did not pipe the suction line to the burner the way Roth shows it so I can't possibly equalize.

    Top draw IMHO causes a lot of issues. Lots of fittings and lots of potential air leaks.

    The suction line has to go into each tank and the tees have to be as Roth shows. All the connections have to be 100% tight to equalize