Main vents, hard to heat area
I’m building owner . Apartment is about 90 years old steam, about 80 feet long , 12 units 6 on each floor . Boiler Weil mc lain maybe 600000 btu, (a bit oversized) the apartments on end of building right next to boiler room (red X on drawing) don’t get as much heat as units at other end of building . Pipes insulated , steam pipes and radiators have proper pitch, radiators in those apartments are double vented Gorton D. So it’s not the apartments. I think it’s the main vents which are a bit of a mess as I’ve experimented with double and triple vents . There are 3 returns . All had one vent on them when I started years ago. As in photos. The building has settled in recent years from to many big trees planted (I had them all removed) I do hear water sloshing in pipe about 50 feet away from boiler but I can’t find any sag in main. My main vents are a mix of Dole and Gorton 1. The apartment next to boiler are about 5f degrees cooler than the other side. How should I proceed?
Comments
-
If I was in your position, I would draw up a detailed sketch of the piping. I'm a visual person so that would help me to know how to attack the problem.
As 1940s book on steam heat said (I'm paraphrasing here): "you can't control heat distribution without adjustable vents." By putting the largest D vent on all rads you basically deny yourself ability to heat up some rad first. Your furthest rad indeed should be D but those closer to the boiler can be much smaller opening. Again this is theory only and proper sketch of your piping will reveal reality (sometimes rads physically closest to the boiler are actually far based on pipe run).
»»» See my steam heat YouTube videos:
https://www.youtube.com/@HeatingBlog0 -
Also, those Dole vents are rather slow. You're probably looking at a bunch of Gorton #2 vents. But let's see the piping diagram- include the length and diameter of each steam main.
1 -
I did not use Gorton D on all radiators . I use from zero vent a blocked shut off radiator , and Gorton 3/4/5/6/C/D . On hot radiators I use the top vent only a Gorton 3, (which is actually a Gorton 4 with foil tape over the hole and I use a small pin to make the smallest hole possible. On coldest radiator I use top and middle vent and Gorton D, and I’ve even drilled them out larger. I do know how to balance radiators . It’s the mains . Or I just need bigger radiators. It was balanced last year but these end units have always been a problem . I use a YoLink temp monitor system that is all calibrated to .05f , it’s a great temperature monitor system that goes 2400 feet not like Bluetooth or WiFi .
0 -
You need more main venting. The idea is to get steam TO the takeoffs for the end radiators faster.
0 -
if you're hearing sloshing the boiler is probably throwing water in to the mains. how stable is the water line when it is steaming?
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 136 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements