Five Aqara W200 thermostats on Taco ZVC405-4: transformer capacity and separate power?

Options

I'm considering five Aqara W200 thermostats for a heat-only hydronic baseboard system:

• Taco ZVC405-4 controller, two factory 40VA transformers.

• Five Taco Zone Sentry Z075P2-2 valves.

• One transformer supplies zones 1-3; the other supplies zones 4-5.• Existing thermostat connections use R and W. Usable spare conductors back to the controller haven't been confirmed.

Aqara says to allow 6VA per W200, including startup and peaks, and keep the combined valve/thermostat load within 80% of each transformer's rating. That adds 18VA to the three-zone bank and 12VA to the two-zone bank.

Aqara doesn't recommend third-party common-maker/add-a-wire devices. Their own adapter requires G/Y connections, which these heat-only thermostat connections don't have.

I'm trying to resolve two questions:

  1. Can the existing transformers support these loads, including simultaneous Zone Sentry charging after a power outage? How does Taco's published allowance of up to 12 Zone Sentry valves per 40VA transformer account for charging demand? I'd appreciate manufacturer guidance or actual measurements rather than assuming nameplate loads tell the whole story.

If the shared transformers aren't sufficient, is there a supported separate 24VAC power arrangement for the W200s while retaining control of these valves? What isolation equipment or manufacturer-approved wiring diagram would be appropriate?

I've asked Taco about capacity and Aqara about separate power; those questions remain unanswered. Any experience with this particular controller and valve combination would help.