Boiler help Armstrong pro air

Options

I came across your discussions about outdoor wood boilers and increasing ECM furnace blower speeds using isolation relays.

I’m experiencing the same problem and would greatly appreciate your expertise.

My equipment:

● Armstrong furnace: A96US2V135D20S-02

● Armstrong AC: 4SCU20LX148P-1

● Honeywell T10 Pro smart thermostat

● Central Boiler Classic 6048 outdoor wood boiler

● Water-to-air heat exchanger

I’ve restored automatic wood heating using a secondary thermostat connected to R and G, but the blower speed is insufficient. Testing confirmed that a cooling demand produces substantially higher airflow.

My goal is to use one smart thermostat with higher blower speed for wood heating, automatic propane backup and proper AC compressor isolation.

Would you be willing to help me design a wiring diagram and recommend the necessary relays and aquastat?

I have detailed pictures of all the equipment, wiring, control boards and factory schematics available.

Thank you very much for your time and expertise.

God bless,

George Bush
Belgium, Wisconsin

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,067
    edited November 24

    I have done this with ECM blower equipped air handlers. let me look for my notes on this.

    This comment was on topic regarding getting the variable-speed blower to stop blowing cold air and operate at the higher speed.

    Let me look at your situation. It is different and you may want to do it a little differently. Basically using a wood boiler you don't want to have the boiler heating up without using that heat somewhere. What is heating your Domestic Hot Water? That could be a place to dump extra heat from your wood stove. The other thing is to overheat your home to 75° or more so you don't end up with dumping excess heat on the ground outside.

    It will take some time to get used to your wood stove and how to feed it so you are not wasting heat. but even getting it perfect you may still need ot experience indoor temperatures over 75° rather than waste that heat somewhere that it does you no good.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,067
    edited November 24

    First thing to get the fan operating at a higher speed you need to fool the appliance into believing that it is heating or cooling on stage 2 in order to get the highest fan speed. That can be done with a wire from the thermostat W1 terminal to a heating relay to tell the control that it should be heating on stage 2 and make sure the gas valve does not send gas to the heat exchanger. Or you fool the control on the appliance to believe it is cooling on stage 2 without allowing the compressor to operate.

    Once you have decided which way you want to go, you then configure W2 of the thermostat to operate the heating system as usual in the event that you don't get any heat from the wood boiler. Then stage 2 will kick in for heating with Gas. This will take at least 2 relays to accomplish that, maybe even 3 relays. See what you are interested in and I will create a control system for you to start with.

    EDIT:

    After looking at your heating furnace wiring diagram and control system, I think it will be easier to fool the control to operate at stage 2 cooling speed and not allow the compressor to operate. That can be done with one heat relay that has double poll double throw contacts (DPDT). You will need another temperature switch to enable the hot water from the wood stove to keep the blower operational even if the room thermostat is satisfied, in order to use up any heat the wood boiler has to offer. This will override the thermostat so to control the hopme temperature from over heating you will need to learn how to feed the wood stove in such a way as to keep the home from overheating too much. You may end up with an 85° home some days until you get it right. You may need to run around the hot house with no close on on those days.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?