Rube Goldberg indirect.
I have been working on getting the most out of an indirect on an A2WHP (best is get a HPWH, but I already own the bits).
Using a plate HX, this sits on my primary loop which is in constant circ with ODR. The charge pump is driven by the 3 way valve control signal from the A2WHP when it goes into DHW mode (same signal also disables all space heat).
This setup accomplishes a couple of things. Any cold water draw is flows backward through the HX and is pre-heated to space heat temp. Since this uses low temperature space heat, the COP is much higher. It also back-flushes the heat exchanger.
The challenge I had with a simple HX/pump setup is it charge pump flow rate was always a compromise. Flow rate too high, outlet temp would be too low and it would actually cool the top of the tank off (A2WHP output at high temp is much less than a modcon). If too low, then the unit would have to run at higher temp for long time to re-heat the tank (bad for COP).
In this setup, when there is a DWH recharge cycle, the charge pump runs into the mix port of a thermostatic mix valve. If the water temp is low, the mix valve diverts to the bottom of the tank which avoids breaking stratification. Once the bottom of the tank warms up and the outlet temp increases, the valve switches over and heats up the top of the tank. This way, the pump can run at max flow to get the most out of the supplied heat.
It only needs a couple of additional easy to get parts and works much better.
Comments
-
Interesting
On cold water draw, what prevents flow from going through circ path and avoiding prewarming of through heat exchanger. I'm assuming some cold flow will go through both paths.
….oh I see the fine print now. Flow switch to stop circulator. But does it close off that circ return path?
When your water heater calls for heat, what temp fluid does the awhp send to HEx?
Just a bit complex 😅
0 -
for your own system it makes sense. might be a hard $$ sell for a customer.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 136 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements