Boiler Positioning Question
Hi all, I hope to be replacing my old Utica (pictured) with an EK1 Frontier (.85 nozzle) at some point.
As I'll be close to the 'upper limit' of a 5.5 " liner, I'm hoping to avoid adding any unnecessary bends to the vent piping. I have two 90 degree bends right now. The vent goes up 3.5 feet, then ~2 feet horizontal to an 18' 2-ply smoothwall stainless liner (insulated).
Assuming that I'm looking at this correctly, I see a few options and hoping you can help rule some out.
a) If I want to directly line things up I'd have to shift the boiler 8" to the left, but this would result in the boiler sitting in front of the right-most pipe coming out of the foundation, ending between it and the middle pipe. ls there a certain distance that I could provide between the back of the boiler and the pipe that would allow a plumber to comfortably access those pipes if ever needed, or is this just a terrible option?
If the new boiler sits right where the Utica sits, I need to shift the vent 8" to the right and 2" back in order to line things up with the vent on the EK1. The horizontal section of galvanized vent is 8.75" long and can be cut if needed, and since the EK1 is shallow, it can shift a bit forward as well.
b) The simplest option would be to turn the 90 degree bend 45 degrees to the right and then line it up with a 45 that comes off the vertical from the EK1, this would result in the addition of one 45 degree bend.
c) A more involved option would be to try to replace the 90 with a 45, which could then be angled diagonally downward towards the 2nd 45 that sits on top of the vertical from the EK1. This would require some combination of moving the EK1 significantly away from the back wall and dramatically cutting down the horizontal section of vent pipe.
Anyway, I'm probably overthinking this
but once the boiler is in place it ain't moving so I want to do it right the first time.
Any suggestions would be appreciated, thanks.
Comments
-
I think you are overthinking it. EK Frontier - 1 has a 4" flue opening and you are connecting to a 5.5" liner that usually has a 6" sleeve at the bottom end of the liner. Connect the 4" vent on the boiler to the 6" base of the liner with a 4" single wall connector. if you were to angle the single wall pipe with a 4" adjustable elbow there will be less than a 45° turn out of the boiler and only one 90° turn to the base of the chimney liner. Use a 4 x 6 increaser to make that final connection to the liner.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Hi Ed, thanks for the helpful reply and yes, I'm overthinking as usual :)
A few questions: I was counting the turn at the tee inside the wall as a 90 degree bend and reducing liner capacity by 10%: am I wrong, and that turn doesn't figure into the calculation for liner size? If not, that's great.
Regarding the elbow coming immediately off the EK1: I didn't realize that there were adjustable elbows but that makes a lot of sense, and placing it at the very bottom minimizes the angle.
0 -
No issue at all. The boiler can be set so the flue offsets left after the rise. It doesn't need to be two 90° turns. Get the rise and face an elbow 45° from the chimney breach. Then 45° into the breach. EK wants to increase to 5 inch after it exits the boiler on the EK-1 Frontier.
0 -
Hi HVACNUT, my concern with putting a 45 at the end of the 9" horizontal (I assume 'breach') pipe is that if you point the 45 horizontally to the right and run the required 8", is this not also running 8" into the room/ away from the wall?
If so, then once you angle it downward to mate with another 45 (coming from the EK1) I think it would add a few more inches to that figure (though I don't know how you guys figure that).
In other words, wouldn't a 45 at the end of the 9" breach pipe force me to move the boiler 11 inches or so into the room (which I can't do) , or cut the 9" breach pipe down to 2" (can you do that?) and then move the boiler a few inches?
Having said that, please see my reply to Ed, as I was reducing capacity of the liner by 10% based on the 90 degree turn inside the wall where the tee meets the liner, and I might have been wrong in doing that, which gives me some breathing room.
If I was wrong about the 10% reduction, and I'm right about a 45 forcing things to move into the room, then I think the adjustable elbow at the EK1 would work well.
I've heard about EK wanting to adapt to 5" right away, though I wonder if adapting to 6 right away, esp if you're concerned about draft, might be even better? I assume this could be done immediately after the adjustable elbow.
Thanks for the reply, I'd like to know what you think about what I wrote.
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 136 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements